OK I am stuck on a job with (1) 4~20 mA transmitter and (6) devices on the loop, 48 VDC power supply.
OK dumb math
6 devices 4 mA =6VDC drop on the loop.
6 devices 20 mA=30VDC drop on the loop.
My transmitter is only rated for a 40 VDC max input. If my loop ever gets to 4 mA I will have an over-voltage condition.
So I need to a 6 Volt drop to ensure I don't have an over-voltage condition if they take a few devices out of the loop. How do I get there.
If I do Ohm's law R=V/I
6 V/ 0.004 A = 1500 Ohm's
6V / 0.02A = 300 ohm's
I probably didn't explain this well I am tired
do it the other way -
 V -----[ RES ]------[4 ~ 20mA Loop]------ V
Your resistance needs to see an 8 volt drop to maintain Maximun 40 Vdc. (around 400 Ohm)
I recomend you calculate it for a lesser voltage (32 or 24)
no create 6 Parallel circuits - the same
Ian The transmitter has a minimum voltage of 10VDC so If I get a 20mA signal I will drop 30 VDC. See the fine line I am trying to balance?
By using a resistance is series concentrate on the Value of R
the Supply Voltage will be 48 V
Voltage Drop on R is Max Current x R = 0.004 x 2000 = 8V Drop (40 Vs max)
or 0.02 x 2000 = 40 Volt Drop (10 Vs Min)
No issue with minimum voltage.
I would recomend you consider a Zener Diode to Prevent an Over voltage Spike
Hi Mickey - they don't appear to be rated for 48 Vdc (30 Vdc Max)
He would not need 48VDC if he used one/couple of those. I think the only reason for the increased voltage was to support the increased load.
Mickey is correct the original guys used a 48VDC supply because the had so many devices in series that the caused a significant voltage drop on the loop. I got the job of a just replacing the existing trip alarms with new ones. We all know how that goes the system was installed in 1999 so everyone of the alarms are obsolete and we had to get new devices.
I dropped the ball and didn't do a loop calculation because hey we are just replacing the alarms.
you all know what these jobs are like.
Your probably right - I was remembering that some servo systems use 48V and their power supplies don't have a lower voltage available
the resistor Calc's I have given will work Fine -
If Possible make 6 seperate loops and use 6 seperate Series CCts
Ahh - Me Not Understand - Me Stupid -
It may still work Out - I'll get back to you shortly
I have a quick question, I want to verify the data that this online calculator provides. a company installed some equipment for me and used 14-3...
5,692
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,155
Customer has a 12VDC solenoid. I have a 24VDC DO. Solenoid specs. 12VDC 4.7W P=IV= 4.7 = 12 * I I=0.39A If I want to drop the 24V to 12V...
23
5,743
I have a customer that is in a poorly wired warehouse . He has receptacles that are feed with #12 about 420 ' away. At times he is down to 95 vac...
4,010
what is the formula to calculate DC volage drop? Is it different than AC voltage drop. Thanks in advance.
3,614