Drop voltage for solenoid - Need help with obvious
Actually the resistor in series might get you in trouble. The solenoid is an inductor, not a resistor, and therefore the current/voltage relationship is different. Like a motor, the solenoid pull is dependent on current, not voltage. And, if you look at the specs, you will see that the operating current requirement is different than the holding current. I'd check this out before I get too far into this.
I would also just use a relay to get the job done until the proper parts come in.. But i would repair it with the correct part as soon as it comes in to me relays are just another point of failure down the road....
Everyone who keeps saying use relay, I don't have 12VDC to begin with, so an interposing relay is not going to help any.
If by any chance you have to open multiple solenoids at once, you could put two in series.
Exact. The solenoid will see a lot less than 12v at time of inrush and may not get enough magnetic power to move. It will probably remain in a ''half closed'' state and burns...
Adding the capacitor to by pass the resistor on the pulse would help.
I would choost a 10w resistor instead to keep room.
This would be nice for an electronic class room but for an industrial process, it is not a good solution. Resistors and other small electronic parts aren't really welcome in the field.
First there isn't much support or terminal connection for them, so the final result won't be visually nice.
Second, This isn't usual so if someone else play around it, it will have a hard time to figure it out.
Third If power supply or valve get replaced, it won't come with a new resistor so good chances that it will be discarted and 12v valve connected to 24 directly....
Unless you are the only one playing with it and you plan to live forever, if you do it make sure to comment it on the drawings etc...
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,154
I have a customer that is in a poorly wired warehouse . He has receptacles that are feed with #12 about 420 ' away. At times he is down to 95 vac...
4,009
OK I am stuck on a job with (1) 4~20 mA transmitter and (6) devices on the loop, 48 VDC power supply. OK dumb math 6 devices 4 mA =6VDC drop on...
30
5,934
I have a quick question, I want to verify the data that this online calculator provides. a company installed some equipment for me and used 14-3...
5,692
what is the formula to calculate DC volage drop? Is it different than AC voltage drop. Thanks in advance.
3,614