DC voltage drop
Not to avoid the question, but what exaclty are you trying to determine. Are you trying to decide on wire size and/or length?
The DC voltage drop is simpler because it does not have to consider an AC power factor. On an AC circuit, if the power factor is not 1, then the effects of reactance must be considered (as well as the resistance).
For a DC circuit, a simple calculation of voltage drop would be:
VD = R X CL/1000 X A
where:
R = Resistance of wire (Ohms) per 1000 feet
CL = Circuit Length (distance out to load and back)
A = Total Circuit Load in Amperes
If your wire R value is per 100 feet, then change the 1000 divisor to 100.
You can see that the voltage drop is dependent on how heavy the circuit is loaded (not just the size of the wire and the length). This is a fact often forgotten or ignored.
For an AC single-phase circuit, for "R" in the above formua you have to substitute the effective "Z" (Impedance = Resistance + Reactance) for the circuit power factor.
newguru said:
what is the formula to calculate DC volage drop? Is it different than AC voltage drop. Thanks in advance.
E=I X R in both AC and DC circuits, if it is a purely resistive circuit. If there is reactance, in the AC circuit, then the R will be replaced with XC or XL or Z if you have a combination of resistive and reactive components.
That is the wonderful thing about the rules, once you know them.
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,151
Customer has a 12VDC solenoid. I have a 24VDC DO. Solenoid specs. 12VDC 4.7W P=IV= 4.7 = 12 * I I=0.39A If I want to drop the 24V to 12V...
23
5,738
I have a customer that is in a poorly wired warehouse . He has receptacles that are feed with #12 about 420 ' away. At times he is down to 95 vac...
4,009
OK I am stuck on a job with (1) 4~20 mA transmitter and (6) devices on the loop, 48 VDC power supply. OK dumb math 6 devices 4 mA =6VDC drop on...
30
5,930
I have a quick question, I want to verify the data that this online calculator provides. a company installed some equipment for me and used 14-3...