Siemens S7-300 not going into run mode
Screenshot attached (Post 2)
There may be multiple issues here, but first, this error indicates a problem reading from your analog input card, channel 0. Exact cause is unclear, as your other screenshots look OK.
Create an OB121 and download it. Don't bother adding any logic. This will prevent the transition to STOP. Then look for other errors.
Ate there any other accesses to Input 288? (Options > Reference Data > Display, Cross-References)
Solved !!!!
:D
No cross reference issue (attached image 1)
I think I found the error (attached image 2)
The inputs were all deactivated, once i activated the required inputs and downloaded to the PLC the errors disappear.
I assumed that having them deactivated would have helped the issue not caused it.
Anyways thank-you to everyone who contributed, I am really grateful that all you guys go out of your way to help us (y)(y)🍻:site:
2023-05-05 12_16_24-Ref - [S7 Program(2) (Cross-references) -- Test_Rig_SIMATIC 300 Station_CPU .png 2023-05-05 12_13_34-HW Config - [SIMATIC 300 Station (Configuration) -- Test_Rig].png
The 6ES7-331-7KF00-0XB0 module has square jumper blocks on the side of the module, with a notch to indicate whether the position is A B C or D.
This must match the HW Configuration of the AI module. See attached images.
It is recommended to leave the unused group(s) on the B position.
Now on to your next issue (I'm anticipating it)...
2-wire current analog (2DMU) means power AND signal are on the same 2 wires.
4-wire current analog (4DMU) means power and signal are on separate wires
Most applications I see use 4DMU and not 2DMU.
Module wiring
LoL, you are right mate, there will probably be another issue once I add the comms module I'm sure, but I have definitely got 2 wire transmitters so no issue with that thankfully.
Once again that you for all your help
I've a Siemens S7-300 cpu (with two DI, two DO and one AI) card. The problem is that all the I/O cards have gone into SF (system fault) with solid...
16,480
115
Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
1,470
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
703
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
1,080