Siemens S7-300 not going into run mode
advanced.eic
Aug 2016
Australia
G'day guys,
I am setting up a s7-300 as a test rig for the workshop and when I downloaded the PLC is not going into run mode, I keep getting a parameter assignment error in the CPU.
Any help on fixing the issue would be appreciated
Please show the details of diagnostic messages 1 and 4.
When did this start happening?
What happened just before the problem first occurred?
Maybe there is a discrepancy between the actual hardware and the setup in the TIA project.
List all modules in the rack.
Post a screenshot of the device configuration in TIA.
Not sure how it works with S7-300 in TIA. There is usually a quite precise error diagnostics when you use S7-1500.
(not used to S7-300 in TIA)
The only error now seams to be the attached images.
I can completely remove the analogue input on the card address 288 and the fault disappears and if i move it to another input the fault follows the first addressed analogue input.
Hope that makes sense.
You have a problem with the AO module. If you right click it and do "Online Diagnostics" you should get a more exact error.
I will check it out tomorrow, never though of checking the module has it had no errors directly reported.
Thanks for going out of your way to help mate, highly appreciated 👍
The top left little icon tells you there is a problem (see attached image).
Could be missing 24V or (crazy enough) I've had someone forget to put the "U-shaped" backplane connector that connects the modules to each other. Could be that the module is not firmly seated on the rail or U-shaped connector. Or it's the wrong module selected in the configuration or wrong module installed in the rack.
Total re-write from scratch
I have totally started from scratch for this one trying to find the issue.
All the program does is scales the 5 analogue inputs and does absolutely nothing with them (as basic as I can get to replicate the fault).
I have also change the slot numbers and locations of the modules to no avail.
I have attached screenshots of the modules as requested and also the diagnostics buffer.
Thank-you guys for all your help thus far
P.S. The fault is any showing up when the inputs are configured to do something, if I load just the hardware config, I get no errors??????
Tom
2023-05-04 07_41_30-Siemens  -  C__Users_IT Admin_Desktop_TestRig_Fresh_Start_Project_Fresh_Star.jpg 2023-05-04 07_33_07-Clipboard.png 2023-05-04 07_43_56-Siemens  -  C__Users_IT Admin_Desktop_TestRig_Fresh_Start_Project_Fresh_Star.jpg 2023-05-04 07_43_48-Siemens  -  C__Users_IT Admin_Desktop_TestRig_Fresh_Start_Project_Fresh_Star.jpg 2023-05-04 07_43_05-Siemens  -  C__Users_IT Admin_Desktop_TestRig_Fresh_Start_Project_Fresh_Star.jpg
I've a Siemens S7-300 cpu (with two DI, two DO and one AI) card. The problem is that all the I/O cards have gone into SF (system fault) with solid...
16,480
115
Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
1,469
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
703
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
1,080