PLC Benchmarking
You and I have somewhat different views on the quantity inferred by "slightly".
Probably. :) Since the numbers are there, people can draw their own conclusions.
The logic posted above is running at 103 msec in the L71. What are you seeing?
I have packed the PLC away for today. Maybe I get time to do it tomorrow.
edit: In S7, "TRUE" and "FALSE" are keywords.
1756-L85E v28
MathTest : 6.0
IndexTest : 3.7
BitwiseTest : 2.6
Tried to attach the RSLogix file, but it was too big.
Revised numbers on updated tests for
1769-L18ER v24
MathTest : 348.0
IndexTest : 131
BitwiseTest : 148
I have to say that I was surprised the L24ER was faster. I was thinking the L18 and L24 had the same processor, only more memory and embedded IO.
After seeing the differences in indexing arrays and ANDing, I think the test should be revised:
Math Test stays the same:
Code:
FOR i:=0 TO 99999 DO
	DINTResult:=(Real1*Real2);
END_FOR;
@Archie
What values are you using defaulting Real1 and Real2 too?
Running Math Test on an NJ101
Real1 and Real2 set at 0
32ms
Real1 and Real2 non-zero
89ms
Results + code for S7-1517F
Code:
CASE "TestType" OF
    1:  //indexed multiply with non-zero data - 19ms
        FOR #diIndex := 0 TO 99999 DO
            "dbResult".arData[#diIndex] := REAL_TO_DINT("dbData1".arData[#diIndex] * "dbData2".arData[#diIndex]);
        END_FOR;
    2:  //non indexed multiply with non-zero data - 14.5ms
        #rData1 := 100.0;
        #rData2 := 1000.0;
            #diResult := REAL_TO_DINT(#rData1 * #rData2 );
        END_FOR;
    3:  // some trig functions - 13.5ms
        #rData1 := 0.1;
        #rData2 := 0.2;
            #diResult := REAL_TO_DINT(TAN(#rData1) * TAN(#rData2));
        END_FOR;
    4:  //non indexed multiply with non-zero data, more calcs, for loop smaller - 14.2ms
        #rData1 := 1000.0;
        #rData2 := 100.0;
        FOR #diIndex := 0 TO 9999 DO
            #diResult := REAL_TO_DINT(#rData1 * #rData2);
        END_FOR;
    5:  //non indexed divide with non-zero data - 14.9ms
        #rData1 := 1000.0;
        #rData2 := 100.0;
            #diResult := REAL_TO_DINT(#rData1 / #rData2);
        END_FOR;
    6:  //non indexed multiply with zero data - 7.5ms
        #rData1 := 0.0;
        #rData2 := 0.0;
        END_FOR;
    7:  //Boolean logic - 1ms
            #boolvar_1 := (#boolvar_2 AND #boolvar_3) OR (#boolvar_4 AND #boolvar_5); // logic --(=)
            IF (#boolvar_6 AND #boolvar_7) THEN
                #boolvar_10 := TRUE; // logic --(S)
            END_IF;
            IF (#boolvar_8 OR #boolvar_9) THEN
                #boolvar_10 := FALSE; // logic --(R)
            END_IF;
        END_FOR;
    8:  //Bitwise operation - 1ms
        FOR #diIndex:=0 TO 99999 DO
            #diResult := #diIndex AND 2730; //* Every other bit FOR 12 bits
        END_FOR;
    9: //bubble sort - 26ms
        #Result[0] := 2;
        #Result[999] := -1;
        REPEAT
            #swapped := 0;
            FOR #diIndex := 1 TO 999 DO
                IF (#Result[#diIndex - 1] > #Result[#diIndex]) THEN
                    #Temp := #Result[#diIndex];
                    #Result[#diIndex] := #Result[#diIndex - 1];
                    #Result[#diIndex - 1] := #Temp;
                    #swapped := 1;
                END_IF;
            END_FOR;
        UNTIL (NOT #swapped)
        END_REPEAT;
    10:  //initialise array of data to non-zero values
            "dbData1".arData[#diIndex] := DINT_TO_REAL(#diIndex) / 100.0;
            "dbData2".arData[#diIndex] := DINT_TO_REAL(#diIndex) / 50.0;
        END_FOR;
END_CASE;
Results + code for S7-319F
Code:
FUNCTION fc1:VOID
VAR_TEMP
    i:INT;
    iIndex:INT;
    diIndex:DINT;
    diResult:DINT;
    TestType, temp:INT;
    rData1,rData2:REAL;
    swapped:BOOL;
    boolvar_1:BOOL;
    boolvar_2:BOOL;
    boolvar_3:BOOL;
    boolvar_4:BOOL;
    boolvar_5:BOOL;
    boolvar_6:BOOL;
    boolvar_7:BOOL;
    boolvar_8:BOOL;
    boolvar_9:BOOL;
    boolvar_10:BOOL;
    Result:ARRAY[0..999] OF INT;
END_VAR
testType:=9;
CASE TestType OF
    1:  //indexed multiply with non-zero data - 85ms
        FOR iIndex := 0 TO 9999 DO
            FOR i:=0 TO 9 do
             "dbResult".diData[iIndex] := REAL_TO_DINT("dbData1".arData[iIndex] * "dbData2".arData[iIndex]);
            end_For;
        END_FOR;
    2:  //non indexed multiply with non-zero data - 21ms
        rData1 := 100.0;
        rData2 := 1000.0;
        FOR diIndex := 0 TO 99999 DO
            diResult := REAL_TO_DINT(rData1 * rData2 );
        END_FOR;
    3:  // some trig functions - 160ms
        rData1 := 0.1;
        rData2 := 0.2;
            diResult := REAL_TO_DINT(TAN(rData1) * TAN(rData2));
        END_FOR;
    4:  //non indexed multiply with non-zero data, more calcs, for loop smaller - 14.0ms
        rData1 := 1000.0;
        rData2 := 100.0;
        FOR diIndex := 0 TO 9999 DO
            diResult := REAL_TO_DINT(rData1 * rData2);
        END_FOR;
    5:  //non indexed divide with non-zero data - 25ms
        rData1 := 1000.0;
        rData2 := 100.0;
            diResult := REAL_TO_DINT(rData1 / rData2);
        END_FOR;
    6:  //non indexed multiply with zero data - 21ms
        rData1 := 0.0;
        rData2 := 0.0;
        END_FOR;
    7:  //Boolean logic - 20ms
            boolvar_1 := (boolvar_2 AND boolvar_3) OR (boolvar_4 AND boolvar_5); // logic --(=)
            IF (boolvar_6 AND boolvar_7) THEN
            END_IF;
            IF (boolvar_8 OR boolvar_9) THEN
            END_IF;
        END_FOR;
    8:  //Bitwise operation - 18ms
        FOR diIndex:=0 TO 99999 DO
            diResult := DWORD_TO_DINT(DINT_TO_DWORD(diIndex) AND dw#16#aaa); //* Every other bit FOR 12 bits
        END_FOR;
    9: //bubble sort - 456ms
        Result[0] := 2;
        Result[999] := -1;
        REPEAT
            swapped := 0;
            FOR diIndex := 1 TO 999 DO
                IF (Result[diIndex - 1] > Result[diIndex]) THEN
                    Temp := Result[diIndex];
                    Result[diIndex] := Result[diIndex - 1];
                    Result[diIndex - 1] := Temp;
                    swapped := 1;
                END_IF;
            END_FOR;
        UNTIL (NOT swapped)
        END_REPEAT;
            "dbData1".arData[diIndex] := DINT_TO_REAL(diIndex) / 100.0;
            "dbData2".arData[diIndex] := DINT_TO_REAL(diIndex) / 50.0;
        END_FOR;
END_CASE;
end_function
@Archie
32ms
89ms
That's an interesting finding I never would have expected. I was testing with values at 0. I will revise the math test and run my tests again.
LD, I will use your code for performing my further tests.
Btw, looks like a 1517 easily beats a 319, except for boolean logic !
Have you tested with optimized or non-optimized blocks ?
LD..... Can you post a complete part number or a link to the PLC you tested with. I'm interested in checking out the specs. It looks like quite a fast PLC.
The strange thing is the 319f has a part number of a 318 :confused:
Indeed that is strange. But that is how it is (was). My guess is they planned for a CPU above 319, but then they would run out of numbers since there are only 3 available digits in their system. The PLC above 319 never became reality. Just my (conspiracy) theory.
For your information, list price for the 319F is approx 5700 €, and 1517F is approx 5300 €.
I only reran the non-indexed math test with non-zero numbers. That came in at 298 msec on the L71. This compares with roughly 280 msec for the same test with zero values. Since they were that close in total time I didn't try any of the other variants.
Rockwell is obviously not performing an optimization that other manufacturers are. The S7-1517 shows a 2:1 difference in scan time for zero versus non-zero values.
Keith
224
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
192
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
44
255
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
64