Micrologic 1200 major error
roneal
Nov 2011
jakarta
Dear all
i have problem with micrologic 1200 with 1672-IR4 RTD module, when im plug the 1672-IR4, micrologix 1200 error "The maximum number of input or output words for the expansion I/O system has been exceeded by module 1" but when i unplug the 1672-IR4 module, the PLC was running well..
Please Help
Many Thanks
How many modules do you have connected?
Can you post your program? Its .RSS file ( zip it first). The program that gives you the error.
I see nothing wrong with the I/O configuration. Check and double check the ribbon connections before powering up.
hii
i already check ribbon connection, and also the power on 1762-IR4 module is on, so what the meaning of the error msg?
this is the capture
No, i have 4 module of 1672-ir4
But the 4 module was the same, all major error. But if i unplug the module the plc running well
Oops. I shouldn't post late at night when everything is blurry. I have used a ml1200 and didn't remember. Of course you are correct. I had a system with the max 4 modules and had no trouble.
Its possible that there is something wrong with the module, do you have any other type of module to test in that slot?
I agree, you need to check both the module and the cables/connectors. Also make sure that you haven't bent any pins in the connectors.
Hi we currently have a Micrologic 1200 running an automated saw program. If I plug in a memory module will it automatically write the program to...
1,293
Hey guys, My colleague recently gave me an Allen Bradley micrologix 1200, I only have rslogix micro starter lite on my laptop. From what I can...
3,039
Hello ALL, I have a job coming up where we will be using multiple Rockwell Micrologix 1200 PLC's with on-board ethernet. Can I read their IP...
1,967
Ok, I have a micrologic 1200 plc that I'm tring to get to communicate with a panelview 300. It has a 1761-cbl-pm02-ser.C cable that plugs into the...
2,046
HEllo Experts I am trying to communicate between Wonderware and micrologic though 1761-net-eni module. I installed IO server DASABCIP and try to...
2,986