Rockwell microLogic 1200 Ethernet
Dua Anjing
Feb 2008
under the desk looking for a donut...
435
Hello ALL,
I have a job coming up where we will be using multiple Rockwell Micrologix 1200 PLC's with on-board ethernet. Can I read their IP address from within the PLC programme ? The programme in these 1200's will be Identical except for their IP address's. I am hoping to be able to detect their IP and thus move any location specifif data into a common area that cann be read by a Master PLC.
Now, If you have 1100 or 1400s, there is a status file for the ethernet communications you can read the IP out of yes.
But the only way I know to network the 1200s uses either the 1761-NET-ENI or something similar. I don't believe you can query those from the serial side..
You could be correct Dravik, I'm not sure of processor model etc. but I am sure that it has ethernet on-board. Havn't got the parts yet I'm just trying to get logic etc planned out. So I should be able to find the actual Staus register address inteh CPU manual then ? Thanks for your help
The MicroLogix 1100 and 1400 have an "ES" Function File that includes the Ethernet port status.
Words ES0:09 and ES0:10 include the four octets of the IP Address.
Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
148
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
162
Hi all. What is the purpose of that block (MVM) when used with a 2#1111_1111_1111_1111 mask in that situation? I'm really hoping there is...
167
Customer is adding an extension rack to an existing A22. They wired and powered it up, I configured the new cards in the PLC starting from slot 23...
148
I have got an Rockwell PLC 1769-L36ERMS . I have assigned a IP address to it . But every-time I Reboot the PLC it looses Communication to my PC...
112