ControlLogix 1756-IF16 as 4-20mA
nuflia
Mar 2010
Teesside
Hi ,
hope everyone is doing well,
1756-IF16 Single-ended mode ,Input range;
±10V
0…10V
0…5V
0…20 mA
Can it be used for 4-20mA
or do I need to have 1756-IF16H to get 4-20m
is there anyway 1756-IF16 can be scaled to accept 4-20mA
If your transmitters are 4-20mA then leave them as that.
The PLC card allows for the options of 0-20mA or 4-20mA, hence the configuration of a 4mA minimum as an option.
Most of your plant devices will be 4-20mA as default.
Do the transmitters on site require to be set 0-20mA or they can be left as 4-20mA
2 wire transmitters cannot be ranged to 0-20mA because a 2 wire transmitter uses about 3.5 or 3.6mA of current to operate its own electronics. Without the 3.6mA of current 'below' 4.0mA, a 2 wire transmitter would not operate.
So a 2-18mA or 0-20mA is not doable because there would be no current available to drive the electronics in the transmitter.
3 or 4 wire devices would conceivably be 0-20mA, like an analog output on a PLC's AO card can usually be ranged 0-20mA because power to drive the circuit's components is not part of the loop circuit; the circuit power supply is external.
3 or 4 wire devices would conceivably be 0-20mA, like an analog output on a PLC's AO card can usually be ranged 0-20mA because power to drive the circuit's components is not part of the loop circuit; the circuit power supply is external.[/QUOTE
Thanks for the reply , I've just seen it, i agree with you , the filed instruments are supplied by the approved associated apparatus ,
Hello folks, If I am using the 1756-IF16 Analog Input card to sense a 0 - 20mA input signal, in RSLogix 500, under the Module Properties -> High...
7,267
Is there a way to see what the actual field signal value is going into each channel of the Analog Input I/O card 1756-IF16? In other words, I...
3,675
Hi all, I set 1756-IF16 Analog input card's input range to 0 ~ 20 mA. 20 mA is equal to 20000 Engineering unit. Is it possible to get input more...
5,191
We have a project where we have the 1756-L82Es in redundancy with Remote IO Backplant via EN2TRs. Everything works and is redundant but we can...
384
Hi there! I posted few days ago about a fault i had with my motion. I did some cable check and replacement and it didnt solve my problem yet but...
384