We have a project where we have the 1756-L82Es in redundancy with Remote IO Backplant via EN2TRs.
Everything works and is redundant but we can not get the diagnostic functions of the input and output boards to work. I understand the fault bits can signify things such as on the OB16Ds1 = fault (OpenWire OR FieldPwrLoss OR FuseBlown OR NoLoad OR OutputVerifyFault OR FieldPwrLoss OR CommFault)
and then on the IB16Ds I belive its just Wire Off?.
I have the input module wired up with the leakage resistors and catches the circuit open and closed status just fine with the 24VDC signal, however i would expect to see a fault if the voltage dropped. I see nothing in the module configuration to help with these diagnotsics.
Also my controller tags dont seem to be using the module defined types AB:1756_DI_DC_Diag:I:0 and AB:1756_DO_DC_Diag:I:0
Instead the tags are using the AB:1756_ENET_SLOT:I:0 module defined data types.
Looking for some guidance on what i could be missing as the RA documentation doesnt go over this in great detail.
Using the latest Studio 5000, Latest Frimware in the RM2, EN2TR, and L82E
Any help or guidance would be greatly appreciated.
In the properties for these modules, check to see if they are configured as Rack Optimized. When configured as Rack Optimized you lose all of the diagnostic information. Look at the "Connection" setting on the General page.
Unfortunately this setting cannot be modified. To change it you must delete the module and add it back. When adding it back, make sure you select "Data" instead of Rack Optimized. Rack Optimized is the default setting.
OG
Hi there! I posted few days ago about a fault i had with my motion. I did some cable check and replacement and it didnt solve my problem yet but...
384
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
1,096
PN1651 - ControlLogix 1756-OF8/B modules may exhibit spurious channel 4 through 7 faults. Rockwell just released this and we have an upcoming...
1,083
I was wondering if anyone else has had issues with the PA75 bricking on power ups. We had 2 that were a year old brick on us. 1 bricked when the...
875
I have followed several videos and tutorials that suggest when using the MSG function to enter 2,xxx.xxx.xxx in the Path box in order to connect...
1,413