Interlock, E stop and saftey relay.
neeraj194
Mar 2018
MUMBAI
Hi all i'm a beginner in automation filed I need help with safety relays.
How to integrate interlocking switches(dual channel) and E stop(dual channel) to cut off a single motor using safety relay.
Short answer:
read the manual of the safety-relay. By the way what safety relay do you use? And the other components: interlock switches, E-stops and also the relays?
Fence-guarding and E-stop should be different safety relays (classic safety-relay) but if you use programmable safety-relay (eg pnoz multi) of an safety-relay with safety-IO-cards than you can combine them in one 'safety-relay-system'.
Long answer:
Safety requires some good training provinding you knowledge. eg. The relay('s) should have an NC iintegrated inside the relay (no auxillary-block allowed) and this according to a certain standard (mirror-contacts).
You (and best also others) should make a risc-assessment. A part of this assessment will give you information if this safety-relay should be wired as a single of a redundant system.
Not following the long road can make you end up in jail if something goes wrong.
But here you can ask question but there will be many things to think about if you want to do it professionaly.
Interlocks, E stop and saftey relay.
thank you ivan.maenen for the reply. Actually this is an upcoming project we havent yet selected the components. I've gone through siemens safety relay manuals and what i found was,I need 2 contactor's if I am using E stop in a dual channel manner (using 2 NC contacts ). I'm also using interlocks to cut off the same motor so do i need another set of safety relay and contactors ?
Because interlocking 'fence-guarding' and E-stops serve a safety function: yes.
If you are using classic saftey relays you should use a (third) master-safety-relay. Because of this extra cost you can start to think about a modulair-safety relay if you have 3 or 4 safety functions.
I atteched 3 pdf's:
master-SR_1 and _2: normal situation (1 safty relay, mind you the photo is an example and not belonging to the schematic's involved)
master-SR_3: the master safety relay-concept
Have you done a Risk Assessment on the system? The difference between a PLe Category 1 stop, and PLc Category 0 stop can be a number of parts, and a lot of cost.
What is the outcome of your Risk Assessment? What Stop Category does the application require? Which architecture category does it require?
Hi, I need help adding a new interlock switch to an existing circuit. I have never done on the existing circuit. I did set it up on the...
290
Hi, This morning I attempted to add a good bit of communication between a few of our PLCs. For the most part, everything worked fine, except for...
390
Hi, Had a discussion with a cunsultant about safety and he claimed that for example an Allen Bradley MC1 (two contacts) magnetical non-contact...
1,039
I have a question about process interlock naming. I want to hear opinions, as well as if there is a relevant standard. When naming specific...
689
Working on a robot welding cell today that I have worked on a few of these machines before except this one the fixture air valves are DeviceNet...
1,618