Hi,
This morning I attempted to add a good bit of communication between a few of our PLCs. For the most part, everything worked fine, except for one instance. I have one invalid connection fault between two of the PLCs and I can't figure out what I did wrong.
I added the modules to the ethernet configuration. One has a 1756-L72S Safety Controller, which you can't add manually, so I added the ethernet bridge it is connected to and found it from there. The other one is a 1756-L83E controller and I had no problem adding it to the 1756-L72S.
My tags for the 1756-L72S:
consumed: InterlockFromBBT1 (connection: BBT_Skid:InterlockToCanFiller1)
produced: InterlockToBBT1
Tags for 1756-L83E:
consumed: InterlockFromCanFiller1 (connection: Can_Filler:InterlockToBBT1)
produced: InterlockToCanFiller1
I get the module fault on the 1756-L83E that says (Code 16#0117) Connection Request Error: Invalid connection point. Symbol: InterlockToBBT1.
I've double checked and it looks right to me. I've even erased the tags and started over, but it still gives me the same error.
My only thought maybe there is something extra I have to with connecting the 1756-L72S w/ the ethernet bridge to make the tags work?
Any advice is welcomed. Thanks
This morning I attempted to add a good bit of communication between a few of our PLCs. For the most part, everything worked fine, except for one instance. I have one invalid connection fault between two of the PLCs and I can't figure out what I did wrong.
I added the modules to the ethernet configuration. One has a 1756-L72S Safety Controller, which you can't add manually, so I added the ethernet bridge it is connected to and found it from there. The other one is a 1756-L83E controller and I had no problem adding it to the 1756-L72S.
My tags for the 1756-L72S:
consumed: InterlockFromBBT1 (connection: BBT_Skid:InterlockToCanFiller1)
produced: InterlockToBBT1
Tags for 1756-L83E:
consumed: InterlockFromCanFiller1 (connection: Can_Filler:InterlockToBBT1)
produced: InterlockToCanFiller1
I get the module fault on the 1756-L83E that says (Code 16#0117) Connection Request Error: Invalid connection point. Symbol: InterlockToBBT1.
I've double checked and it looks right to me. I've even erased the tags and started over, but it still gives me the same error.
My only thought maybe there is something extra I have to with connecting the 1756-L72S w/ the ethernet bridge to make the tags work?
Any advice is welcomed. Thanks