4-20ma signal from 1 plc to another
bushmonkee
May 2010
england
Can someone help?
I have AB L32E with a OF4CI analog output card and need to send a 4-20ma signal to another guys PLC with an analog input card. He has 24vdc common and return input signal coming into my OF4CI but we cant get it to work. Any ideas where to start?
Thanks for the reply
I thought the card was isolated. But it could be an idea to get a separate isolator.
Its working the other way round as he is sending me a 4-20 and i am reading it ok on an analog input card.
Here's the wiring for your OF4CI card:
Your reference to power supply common makes no sense to me
Your Iout(+) should go to his AI (+)
Your Iout(-) should go to his AI (-)
With that, you should be able to read a dc voltage across his AI(+) and AI(-). Can you do so?
I have to agree with Dan, it should be a no brainer. It would also help to know the Brand and Model of his Analog Input Card.
Stu......
The notations on the wiring schematic are unreadable.
"Passive" loop powered transmitters or analyzer analog outputs need a connection to a power supply in order to power the current loop.
But your analog output card is 'active', its ouptut is not loop powered.
In fact, the 1769-OF4CI manual has a warning:
Miswiring of the module to an AC/DC source will damage the module.
A-B's claim is that the outputs are isolated, "Compact 1769-OF4CI Isolated Analog Output Module"
As much as I advocate isolation, I don't think ground loops or common mode are the problem, I think the AO wiring is not connecting to an AI on the other end, because AI connections are not called "24vdc common and return input signal" and I find the schematic unreadable.
I suspect that there's some confusion over loop powering the analog output.
The A-B AO is 'active', its outputs are powered from the I/O card.
Passive outputs are loop powered, like below, where S+, S(-) are an analog input:
The A_B Analog Output is not passive, it does not need or want a power supply in the loop it is driving.
I agree. All the more reason to isolate it from the outside world (whatever it is the OP is connecting it to).
We need both side connections to figure it out...an multimeter with a working MA scale (Must of the time the fuse is blown...)
Making sure your module is well configured is needed and check is the card give something and if yes look at the other end with the other side disconnected...if there still 4-20mA signal your side is proved healty and you can stop there or help the other guy...
Your AB isolated card is a sourcing device and should be connected this way on the other side....no other powersupply inline needed and maybe you need to referrence your Analog- signal to his VDC negative reference....
This is why an isolator is suggested, it can work without but if something wrong happend in the other side, your isolated input will blow up and you will need to replace the whole card even if your PLC remain healty
Hi; I have installed a temperature and humidity sensor Autonics THD-R-C which gives 4-20mA signal out. The signal is connected with Fatek...
2,779
Help me ! noise signal plc ? How to prevent noise for plc?
1,893
Hello, first post here and have a puzzling issue. I have recently been troubleshooting a PLC for a client that gets a 4-20mA (24VDC) signal from...
21
6,556
I'm trying to hijack a laser's analog signal from a Modicon to a CLX5000. I ran the wires and did the hook up as normal parallelling in with the...
17,525
Hey folks, I have a situation where I need to connect a 4-20mA transmitter to an AI card that only does 0-20mA. On top of that it only has 8 bit...
2,445