PLC analog input output rate
tom2378
Guest
T
Hi All,
some PLC analog input modules allow the user to program the output rate from 10Hz to 50/60Hz to 1Khz. I understand why somebody might want to select 50/60Hz to reduce 50/60Hz noise. But why would anybody want to select the higher output rate of 1Khz in cases where the 3dB point of the module is specified as low as 17hz.
Put another way is there a reason why you would want information at a much higher rate than the bandwidth suggests is necessary? Is it something subtle to do with PID loops?
thanks
An example is the Foxboro I/A series FBC01 module. Specs on internet by googling FBC01. It is a 32 channel non-isolated analog input 0-20mA input card.
f3dB = 5Hz
Settling time 0.55 seconds.
Conversion time is 6mS.
Why have a 6mS conversion time when settling time is 550mS. This seems to make the conversion time 100 times faster than is actually useful.
If you put a sinus signal on a circuit that dampens the signal at its frequency, then you will still have an output from the circuit, only it will be dampened to a certain degree.
I guess that the 50 og 60 Hz filter is an additional narrow band filter or a lowpass filter that blocks noise from the electrical supply, whereas the 1kHz filter is a lowpass filter to block the large part of noise that has a high frequency content.
Hi all, I’m an electrician with limited knowledge of PLC circuits. Typically I will see simple 2/3/4 wire terminations for transmitters on...
26
1,293
Hi all, I want to catch min piks of an analog signal when digital signal is on(pls see the attached oscillogram). My hardware is 5069-L306ER CPU...
1,013
Hello I have a analog input signal that is bouncing a bit. The PLC card is a 1769-IF8 I changed the input card filter setting from 60hz to 50hz...
4,906
Dear all I am using delta AH530 RS- 2 cpu with devicenet communication and now I am getting problem while configuration of AH6xa-05 which is...
1,054
Hello everyone I got problem during practical. I am using delta plc model:DVP20EX00R2. Problem is that when i give 7v dc supply through bridge...
2,458