I/O access error on S7-300
aamirawan91
Feb 2024
Karachi
33
Hi Siemens guys!
I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and found the following important events:
Event 8 of 10: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 322
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
And
Event 7 of 10: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
FC number: 106
Module address: 264
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
Event 8 is pointed out the address 322 which is an analog output PQW322. I have checked it in the program and it seems to be fine there. Finally i replaced the analog output module containing this address but the issue still persists and sometimes the error is about another address PQW320 which is also in this module. Replacing the module didn't help. I know that adding OB122 will prevent the cpu from stopping but i don't want that. I want the cpu to stop when the issue occurs. I want to eliminiate the root cause of it but can't find the problem. I am attaching the diagnostic buffer here. Please have a look. Is there anyway i can attach the program here too? It's 1.05 mbs.
  • Diagnostic buffer.txt
What kind of module is PQW320/PQW322 ?
Is it in the central rack or on Profibus or Profinet ?
Since no other significant entries appear in the diagnostics buffer, and you have replaced the module already, I think of these possible causes:
  1. Backplane problem. It could be terminal modules are not properly connected, or the terminal module is defective. Or termination module is not properly connected.
  2. Problem on neighboring module manifests on PQW320/PQW322 module..
Hi JesperMP
It's an analog output module: 332-5HF00-0AB0. It's the very last module. It's been replaced but the issue still persists. I have checked the addresses associated with the errors in the program and they seemed to be correctly programmed and configured. I am attaching the HW configuration picture for you.
Try swapping the U-shaped connector between the modules.
edit: If the wiring permits, you can also try to swap the 2 last modules in the hardware configuration, and also swap them in real life.
Jesper is assuming you do not have active back plane adapters. The Active backplane adapter, which allows you to replace modules midway, without stopping the modules further down stream, could be faulty. If you have an active backplane, reseating sometimes works on older systems.
These are common in industries that cannot tolerate shutting down an entire rack for one module swap. The most common method is to use "U" shaped connecters from one module to the next, in a daisy chain.
Update: So, finally I decided to add OB122 to prevent CPU stoppages from time to time but it didn't help. The CPU still stopped after some time and this time due to this:
Event ID 16# 4548
STOP due to I/O management
And right before this event all the events were about IO access error related to all the analog outputs of the last and only analog output module i have. Diagnostic buffer is attached.
  • newDiagnose.txt
Event ID 16# 4548
The FAQ above makes it sound like the message above means there's a backplane error, perhaps low voltage. Agree with the "swap modules and backplane connectors around" plan, to see if that helps.
I might be wrong, but AFAIK the active backplane is only used when ET200M modules are in a redundant Profibus system with an S7-400H as Profibus master.
Wrong. I have seen active backplane on many stand alone S7-300 systems, usually continuous processes, such as chemicals, waste treatment plants and such, any process that required high availability. It is expensive, so not common.
Event ID 16# 4548
All of that tells us what we already know: The CPU cannot access PQW320 or PQW322 sometimes.
Please try what was suggested in #4.
Data Acees Error for Alias A_THMC_REV_POL, controller PLC-1
157
Hi, I am trying to fix an issue with PV600 standard terminal. After changing one alarm message description and downloading to the terminal, I...
1,627
I have an installation that looks like this https://i.imgur.com/uR7hxki.png , everything works perfectly except for the ET200SP module. I looked...
1,877
Hi all, We are having issues with reading the peripheral inputs of a Keyence SR-1000 barcode reader. Although we already have some experience...
3,143
Not sure what the issue is, there is no security enable on the project and I can download and go online normally. If I hit run to try and trace...
1,808