Hi there,
We have panelview plus installation on DH+ network. Recently we moved from PLC 5 to CLX. Due to CIP connection limitations to optimize the network if we use UDT (dump all tags required by the panelview in one chunk) than individual tags, will there be any improvement in the network load ?
Thanks in advance
siv o_O
CIP wont go through DH+. You will need to switch to Ethernet/IP or ControlNet to use CIP. I dont think this will help. Someone correct me if Im wrong
I don't know that blocking up the data in the ControlLogix will help reduce network traffic from the PanelView Plus, although I have never tried this. If you're concerned about loading on the network, you can increase the tag update rate on the PV+ screens (I believe the default update time is 1 second). You might also look at any configured datalogs and see what their update rates are.
I don't know if the PV+ works like the ASB modules, but in an application that has numerous BTR/BTW's to a single ASB module, we had to employ a "message manager" to ensure that only one set occured on a single ASB at a time.
How are your messages conditionalized?
But in general, if your data is in a continuous length of data (like an array), then your messages will implement more efficiently.
PV+ terminal uses up to 5 "CIP connections" to the ControlLogix through the 1756-DHRIO module, but the 1756-DHRIO can only bridge 10 of these CIP Connections according to the technote below
http://rockwellautomation.custhelp.com/app/answers/detail/a_id/52653
we experienced screens don't update with increased number of PV+ terminals. Tags update time can contribute to network traffic. since DH+ is token passing, will continuous block of data reduce traffic? How to monitor the network load ? should the monitoring device (computer) need to be in the same physical layer (DH+)?
I received the following message via PM, and am posting here publicly to help others. ============================================ I had a...
1,058
I'm using Ignition 8.0.9 and am having the following issue: I’m using a UDT with the following members: Setpoint SP_HiLimit SP_LoLimit Within...
2,215
I'm working with Ignition 8.0.7 and am trying to enable/disable certain UDT members based on what PLC the UDT is originating from. I have a...
2,018
I am wondering if this possible. I am trying to automate some of the processes we use by putting them into nested AOI. In the past, we would...
1,994
I want to transfer 4 bits from AB PLC(studio 5000, logix designer) to ABB ROBOT(IRB 1600) , the type of data is DINT and send the data when camera...
1,941