Which appropriate equipment should I use to get water level signal at PLC?
I have installed the WIKA A-10 to obtain the water level signal, and so far, it has been working fine without any problems. Let's see how it performs in the long run.
Problem: the range of the pressure transmitter is quite high considering that the actual level range is only 1 meter of water. Page 2 of the Wika A-10 spec sheet at this link
https://webapps.wika.com/apps/literature/pdf/F015_A10_0309.pdf
shows the lowest available pressure range as 0-15PSIG or approx 10.5 meters water column.
So you're measuring the 1m (wc) of hydrostatic (plus any hydrodynamic pressure from the agitator) with a 10.5m (wc) range using only ~10% of the range of the transmitter.
Maybe there's another model Wika that has a lower range? Pressures in this range are frequently measured with a DP transmitter.
Any pressure transmitter should be isolated from the hot liquid with a dead-headed impulse tube. Being dead-headed, with no flow through it, it will drop a lot of heat and keep the transmitter in a survivable temperature range.
Hi;
I have installed Wika A-10, with range 0-100mbar.
I'm having some difficulty figuring out when an AC line filter would be appropriate for an application. What exactly is being filtered, the...
2,400
Hello experts, can you suggest me what would be appropriate motor protection switch for the following motor (used on a valve drive): 3 phase...
2,015
Hello, I trying to determine if the use of a For/Next Loop is appropriate for my application. 1.) The code in question will check the value of...
2,030
I'm converting 3 plc 5's to L72s. The first was converted last year using version 20. I used version 20 for this year's project, and had planned...
5,494
Hey everyone. I need just about 10 feet of twisted pair shielded cable for a 4-20mA sensor that will be connected to a Koyo Click PLC. I have...
1,754