What is the best way to add 135 PIDE loops to my studio 5000 program?
plctek
May 2022
toronto
23
Hello Everyone,
I have about 135 controller PIDE loops that I need to add to my Studio 5000 and that means I will probably have to create about 135 different PIDE function block routine for each of these loops. Is adding the 135 function blocks the best way of going about this? AS this will take hours.
What is the best and quickest way to do so?
I have imported my list of controller tags from the csv file successfully into studio 5000 but have not yet entered the PV, SP, Kc, etc... for each.
I would like your thought. Thanks!
Honestly, I would create a user defined data type with all of the parameters that you need to use to control or modify control on the PIDE. If all of the controllers are going to be the same style and have the same requirements, build a couple controllers and indirectly address the loops.
I would probably use a UDT where one tag name change will redo the entire routine. Develop the routine one time in the main application. Export the routine and import to a scratch project in another Studio instance. In the scratch project, rename the tag(s) and routine and copy paste to the main project. Rename and copy - paste again and again and again…
I’m not proficient enough with Python to export the project to .L5K and make a script to duplicate the routine with generated routine and tag names, but some people are.
word doc
an idea
build the PIDE. Name the tags XXXX_1 for example.
verify the rung
double click on the rung which will give you the rung in TEXT.
copy and paste that to a word doc
copy and paste your rung text. Find /replace text _1 with _2
repeat.
paste the rungs back into the ladder.
[Rocks back and forth, weeping quietly]
The PIDE instruction is only available in the Function Block Diagram language in Studio 5000, so copying/pasting or Importing numerous instances from a text-format file is a little more complicated than doing so in a Relay Ladder Logic routine. I would go about it by exporting and importing the FBD routines in *.L5X format.
Using your favorite scripting language to increment up the definitions for each tag and instance of the instruction's PIDE-type tag is pretty straightforward.
Figuring out exactly where you want them to appear in the FBD Sheet is more complicated. You might want to make a group of them, then duplicate/import them by Sheet.
Or you could export a FBD Routine, then Import it and re-number the tags that are new each time because they'll be detected as collisions with the existing ones.
I believe there is a ladder version of the PIDE instruction the the PlantPax library.
You can create a ladder AOI that wraps the FB PIDE instruction, and possibly more FB logic depending on your application. Of course, that would require ladder routine(s) to implement the control loops.
I have examples from Logix 500 of how to do a slow increase to the speed reference value, while the operator is holding down a button on the HMI...
1,572
V 10.00.01 Patch 9 I was wanting to make an analog process variable display global object but I guess that is not a good idea. We are doing this...
4,946
Hi, My boss just ask me to convert all add on instructions into normal rungs. Currently, it is add ons in add ons.......... I am just wondering...
2,594
Morning everyone, I know this sounds trivial (but I haven't done it in a long time) but what is the best way to add a PLC card to a running...
5,057
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
567