Utility Transformer Clarification
RRoc
Jan 2017
California
45
My Pump Station Load is listed below and the Main Utility Transformer Supplying this load is 150KVA. From adding up all the current draw. The Pump Station Load is greater than the Secondary Transformer FLA. The Utility Engineer informed although the FLA has been exceeded the Operational Limits of the transformer has not. Can someone explain why this is ok?
Pump Station Load
50HP, Current Draw = 65
15HP, Current Draw = 21
25HP, Current Draw = 34
2HP, Current Draw = 3.4
Total = 274.4
Utility Transformer
Pri Volt: 16.34 KV, Secondary Volt: 480VAC
Rating: 150KVA, Secondary FLA: 180 FLA
@T_Gibbs: Yes all motors are running at the same time.
@James_Mcquade: See picture attached. This is all the info that was given to me. It's a typical Utility Transformer that is owned by the Electric company that supplies the pump station I am analyzing.
My guess is that the motors are not drawing rated power. This is common. Pumps only draw full power at rated flow and head, and the motor is usually sized above the rated power draw.
That was my thought, too. The amps that the OP has listed are from the NEC chart. Motors rarely pull as much as the chart.
Do you have VSDs on your pumps?
It is possible that the rating is to keep the temperature of the transformer down but also to keep the voltage distortion low.
As you are the only customer, and you are just running motors, they probably don't care about voltage distortion as much.
Your motors have a total of 207 horsepower, which is 154KW. I doubt all your motors are 100% loaded and as long as your power factor is not aweful, you are right at the rating of the 150KVA transformer. Generally, the utilities only stock specific sizes of transformers, so i bet the next size they install is 300KVA which costs more a lot more and is most likely not needed.
I ran this past a lineman friend of mine.
He said pole cans can generally run 200% of name plate, sustained with a good breeze. 300% for short spans.
I suspect the utility engineer knows this and knows that even if you pulled 100%, you're barely breaking the name plate on the can, that can supply a good bit more.
My father worked for a utility company that sized all their oil filled pole cans at 200% as well. Pad-mount were still only 100% though.
Also, he used the following method for sizing transformers:
If it burned up and had been installed for 20 years, he replaced it with the same size transformer.
If it burned up and it had been installed for very long, he replaced it with the next size up.
If you are pulling over 150 kVA you may also need to be concerned about the cables from the transformer secondaries to your building's power distribution center, they are probably sized to the transformer and may not have the same access to free air as the transformer and not take as kindly to the excess current.
I'm running into a problem when trying to use the RSLinx Backup Restore Utility where it throws an error when it tries to restore a backup. The...
631
Hello all, been a while. I am unable to open Transfer Utility as a stand alone or threw FT View Studio. I have reinstalled FT View Studio, Linx...
1,461
Hello, I am stumped with logging into the remote directory located on a server setup with a Network Distributed Application. I can't seem to get...
1,142
I have FTView Version 11 running on Windows 10 and I can't upload or download to any Panelview. I get the "Source selected is not a valid device"...
3,889
Hello, I am trying to upload a PanelView program using ME Transfer Utility using a A-B 1747-UIC, Ser. A, Rev. D, Frn. 1.3. PanelView info: Cat #...
2,271