Hi fellow Geeks :)
I am about to make a project, that needs to expand over time. So i am wondering whether it is possible to make all connection between PLC(s7-1500
) and HMI(comfort) throu a OPC UA server. So both my PLC and HMI runs as Clients.
Just to make it all a bit more interesting I have never worked with OPC before, so i would like to make some test-simulation via PLCSIM 15.1. to make sure i have done my job.
Does anyone have a good idea for a server i can test with?
Regards,
Lars
Hej Lars.
One side has to be client and the other server. You cannot have both being clients.
You cannot simulate OPC UA with 'regular' PLCSIM.
PLCSIM advanced should support OPC UA, but I have never tried it.
Also, be warned that the OPC UA Server on Siemens CPUs is far less performant than a 'regular' S7 Connection.
You can play around with this Wizard for estimating the transmission time for OPC UA data by an OPC Server on the S7 CPU:
https://www.automation.siemens.com/perfdata/perfdata.aspx?version=34&lang=en
For a lot of data and using Siemens components I would go with a regular S7 connection.
Siemens S7/TIA v18: "Remote" updates/bug fixes to PLC code & HMI screens..... Hi, The PLC application I'm working on will soon be delivered to...
607
I'm a bit lost. I don't understand why my HMI (Simatic 1200) is not recognising any PLC tags. From the ethernet comms page , all seems OK. Yet...
2,245
Sorry for the basic question: At the moment, the PLC [S7-1200] is connected to a laptop (contains TIA Portal) via the ethernet port. When I add...
1,553
I have HMI MP277 10" Touch and need to connect it with a S7-300 PLC on Profibus NETWORK - I am using TIA Portal V13 and tried to use the Device...
1,046
Yo!!! I have a weird one. I am drawing a simple HMI for a machine to allow the maintenance team to calibrate a scale without needing to get the...
1,513