Hi every one
What is the basis on which a motor star/delta starter is chosen?
I mean is it necessary to use star delta with every motor ?
and what are the correct rules for sizing contactors, overloads and circuit breakers for a star delta circuit?
Regards
Hello mosama.
There are two reasons why one would chose to use a star-delta starter.
1. To reduce the current peak when starting a large asyncronous AC motor.
2. To reduce the torque at the moment of startup. This to avoid mechanical damage or wear.
How to dimension star delta starter:
http://www.plctalk.com/qanda/showthread.php?t=30552
Nowadays, the smallest star-delta starters are dropped in favor of low-cost soft-starters.
Thanks JesperMP for your very quick reply
So I use star delta with every motor or there is a limit for motor KW to use star delta?
So I use star delta with every moto[..]
As long as there are all 6 leads from the 3 windings are available in the motor terminal box, then you can start by star-delta. But that does not mean you must. It depends on if you have to limit the current peak or the torque.
[..] or there is a limit for motor KW to use star delta?
In principle, there is no lower limit.
In some countries, the Star-Delta start is only used for motors over 5.5KW, but there are some applications, where a Star-Delta start should not be used (when you need high starting torque).
Hi all, Got a customer who's asked me to look at a new machine they've gotten in which they're having trouble starting. It's a brand new...
4,298
Without going into a lot of detail, 150 hp motor with a Star/Delta Start how much time on Star before switching to Delta. This is a compressor, I...
2,030
Star Delta Starter with Timer Relay or with PLC Timer. Any preferences? Any reasons one way or another?
4,458
A dust collector blower fan motor 18kW, previously run by a star-delta starter, has been replaced with a VFD( Brand: LS, Model: SV-iP5A). Our...
38
11,825
Reversing Star Delta Starter Hello everyone, I have acquired a used Milling Machine in need of a retrofit all wiring has been...
10,459