Siemens s7-300 profibus controlling vacon
I start the drive as follows:
1) Startup the drive = W#16#0 in controlword and 0 in "speed setpoint"
Drive gives status bit "Drive Run"
2) Get the drive ready to operation = W#16#47E in controlword and 0 in speed setpoint
Drive gives status bit "Drive Run", "Control PLC" and "Drive ready"
3) Start the motor = W#16#47F in controlword and the setpoint in "speed setpoint"
Stop the motor = go back to 2)
I attach the bit in the statusword, if you don't have / use the same names
Thank you Jera and lare.
When i tryed to start the vacon drive from "vacon Live" software the vfd gets fault 8. Which is "system fault".. could the drive be broken?
It is possible.
From vacon manual:
Fault code 8 / Operaton malfunction or Defective component
How to correct the fault
Reset the fault and start the drive again.
If the fault shows again, ask instructions from the distributor near to you
Dear Superiors,📚:wizard: I'm new for s7-300 and yaskawa v1000 drives communication via profibus. My aim is to find how to run the drive or...
1,774
Hi all, Got a client who has requested a SCADA system for downtime tracking and so on. Right now, they want to implement it as a standalone...
20
7,826
Hello Guys, I have s7-315-2 PN/DP with integrated DP. I have no CP module. PLC should be DP master. ON other side there is basler device DECS250...
3,490
Hi guys, Tomorrow I'm heading down to take a look at an existing SCADA system that has failed, and I was wondering if anyone had some suggestions...
18
12,834
Hello, I'm trying to configure Profibus communications between a CPU315-2 PN/DP and a Parker 590 DC drive fitted with a L5353 profibus card. I've...
12,094