Siemens S7-200 / Step-7 Microwin
Sickify
Jan 2015
Edmonton
Good Morning,
Hoping someone with some Siemens experience can give me a hand with this one.
Customer has a S7-200 cpu, which has a 6GK7 243-1EX01-0XEO ethernet module attached.
Initially I connected to the PLC and performed an upload using the USB/PPI cable 6ES7 901-3DB30-0XA0, when performing the upload the software warned me that I should communicate over ethernet or it would not upload all module configuration.
Once I had the program uploaded I was able to check the IP address of the ethernet module (172.16.2.130)
With my laptop set to 172.16.2.253 I connected to a non-managed switch that is connected to the ethernet module. When doing an upload, the warning about not getting all the module configuration was gone, however it would upload the PLC program, then try and connect to the ethernet module(??) and give a communication fault.
Trying to perform a download would give a warning about mismatching configuration wizards.
Here are the part numbers I have for this PLC:
216-2AD23-0XB0
6GK7 243-1EX01-0XE0
231-7PB22-0XA0
235-0KD22-0XA0
EM232 Relay
222-1HF22-0XA0
Hey All, We recently acquired a new used machine off the surplus market. there are two sections to the machine, each with its own PLC/HMI and...
46
11,968
i am using siemens s7 1200 v12 i wrote ladder logic for my project i just want to draw block diagram of my system in pc station . in siemens...
3,197
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
287
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
151
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
195
