Rockwell GuardLogix 5580
Jun 2017
Lisbon
24
Hi...
I have what is so-called "Limit Values" placed in the Safety PLC. These values ​​were written in REAL safety tags format.
It turns out that, after the Safety function on PLC be "closed" (Safety blocked) I cannot update them via SCADA writing.
I understand why this isn't possible, it is the Safety function itself does not allow it.
Is there any way to achieve this? Be able to update these tags via SCADA?
" from Rockwell GuardLogix manual:
The safety-lock feature applies only to safety components, such as the safety task, safety programs, safety routines, safety tags, safety Add-On Instructions, safety I/O, and safety
signature."
Thank you!
3B
:geek:
You can use the Map Safety Tag function. Have your SACDA write to PLC Global tags and then Map the Global tag to the Safety tags. The data will pass from the Global tags to the Safety tags. See attached images.
You can use the Map Safety Tag function. Have your SCADA write to PLC Global tags and then Map the Global tag to the Safety tags. The data will pass from the Global tags to the Safety tags. See attached images.
You can (though you will have to unlock the safety to do this) but in almost 100% of cases you absolutely should never do this.
No matter what precautions you take, the moment you expose a safety limit to be able to be changed by non-safety code, you no longer have a safety function. Even if you place limits on the SCADA entry field, there's nothing to stop me from accidentally fat-fingering a change to the non-safety tag in Logix and accidentally setting the overtemperature cut out to 10909 degrees instead of 100 degrees.
I have passed editted limits via mapping but the safety task tested the value and only used what was called out usable/valid/safe in the risk assessment.
Background for the question: A service man from a sub-supplier has made changes onsite to a Siemens PLC and HMI program. He has not made a backup...
301
Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
178
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
182
Hi all. What is the purpose of that block (MVM) when used with a 2#1111_1111_1111_1111 mask in that situation? I'm really hoping there is...
186
Customer is adding an extension rack to an existing A22. They wired and powered it up, I configured the new cards in the PLC starting from slot 23...
163