Powerflex 525 programming
It could be that the plc is recognised it has a different firmware on the drive and doesn’t match the plc program
I’m assuming it’s on a plc , is this just a replacement drive or a new install
Its on a plc, it is a replacement drive.
What is the IP, Subnet, Gateway of your PLC and Drive?
Link solid but flashing Enet indicates that it's on a network but not sending data. makes me think you have an ip issue.
Have you disabled Bootp?
Set Parameter C128 to 1 (default is 2 for bootp, you should see it scroll across the screen for that).
make sure C129,C130,C131,C132 are set to your IP Address C129.C130.C131.C132 (set the IP on those parameters for each octet).
133,134,135,136 are the subnet
and 137,138,139,140 are the gateway. once those are set and you set C128 to 1, it should be using the set IP once it reboots
You also may have comm data link mismatch between PLC and Drive. Was the 525 set up for ADP in the PLC? If so, all you just have to get the IP address into the drive. If not, then you need to go into Logix (assuming your using that with a 525) and download from the PLC to the drive (also assuming your drive was previously configured from Logix). Otherwise, if the old drive is still bootable, and you have a HIM, copy the parameters onto the HIM and dump them into the new drive.
You really need to provide more detailed info as to your setup.
Hello everyone.
I'm new to this too. Don't you have to power cycle the 525 to get the IP address to save?
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
89
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
117
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
107
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
281
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
287