PLEASE help with Analogue converting maths on S7-200 and scaling
STJ
Mar 2008
Grantham
HI all - am hoping someone could help me a little... I am something of a novice and need to sort out my analogue Outs and Ins for a small project...
I am using S7-224 with 4 Analogue INs, 2 Analogue outs.
I am aware of analoue channels being a single word (AQW0 etc)...
The problem I have here is more to do with the maths !! :-(
Would I be correct to assume that 4mA = 650 and 20mA = 32760 ?
I want to send a 4-20mA signal to a K-tron dosing feeder...
Apparently 4mA equates to 50 RPM on the doser which inturn equates to 0.71 Litres/Hour dosed.
20mA equates to 1950 RPM on the doser which inturn equates to 71.0 litres per hour.
If I setup a box on my TP170 HMI screen for an operator to type in what amount of flow they want (ie 35.5 litres/hour) what would the maths and conversions be ? I am struggling with scaling the output values correctly...?
I have to start with REAL because they type in 34.7 etc, then convert to DINT (use ROUND instruction ?) then convert to single word (HOW ?) to paste value into AQW0.. ?
And how on earth do you work out the scaling from what they type in to the correct value to give correct mA to get correct dosing ??
ANY advice or where to look for samples / examples etc GRATEFULLY APPRECIATED !
THANKS !
Steve
Excellent - thanks for the advice - having browsed around a lot, I came across the examples of creating the SCALE library which creates 3 routines that can be called up and accept input variables (locals) and give the relevant output values...
The three routines S_RTR, S_RTI and S_ITR etc are great !! - you just enter the input scale, enter the output scale and where you want to store the result and it does all the maths for you !
Wish I had found it a few days ago ! - have been pulling my hair out trying to scale the correct values
Hopefully you have plenty hair left!!
The example programs as well as the built-in blocks are quite handy.
At least now you know where to look for future projects.
please help me . I have to make this ladder diagram and I can’t figure it out :(
379
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
64
Hello, I am trying to get a Yokogawa Hart pressure Transmitter and a Rosemount Temp Transmitter to read on a 1769-IF4 module on an L33ERM...
394
Please help me, I have solve many week but still not solve it. I found trouble of factory talk studio when I set tag by browse address of OPC...
128
Hello Everyone, i Have im my Industry a Endress & Hauser Promag400 this has a screen that constantly have that error, it says to wait, somebody...
496