Move instruction
May 2019
Indiana
I want to change my vision system program using a micrologix plc. The vision system uses binary inputs, bits 0 thru 7 to determine program #. I want to move N7:3(program # selected in Panelview 800) to O:0.0 word (Micrologix 1200). Vision inputs bit 0 thru bit 7 are wired to Outputs O:0/7 to O:0/14. Using a MVM instruction, I cannot get it to work. If the Vision inputs are wired to PLC outputs O:/0 to O:0/7, all works great on my test unit. The PLC I will be using has a few bad outputs so I had to start at a different address than
O:0/0. I tried using a Multiply instruction (N7:3 times 128 to scale it up, but that didn't work. I know this is kind of long and I have probably missed some details, but I would appreciate any help.
Just shift left 8 places that's assuming the output card is 16 way
or not sure if you can use N regs at bit level on Micro but if you can just map the N bits to the outputs ... N7:3 bit 0 to O:0/7 N7:3 bit 1 to O:0/8 etc.
Sorry I re-read your OP, thought it was from output/8 on but it's 7
Mask 16320 will move only bits 7 through 14 and leave the rest
Open calculator on your computer and change to programming mode, handy for checking masks in hex dec oct and binary.
Let me see if I have got this right you have a word with the lower 8 bits as a recipe and you move the whole word into an output card but only use bits 0-7
try the SWP function
No parky he has bad outputs within the 0-7 range so can't use that, still wanting to use whatever good outputs are left MVM would be my choice
Sorry what I meant if originally he used 0-7 by doing a swap on the N word then moving it to the output card this will change bits 0-7 to 8-15
That is what I meant.
Sorry, I was 1 bit typo out, the mask should be 32640 for bits 7 through 14.
Tested on a mlx 1000, if it runs on that it'll run on anything.
You'll want to put in a check that your source value doesn't exceed 32640, or it will error on math overflow.
Hi All, I am using 2 MOVE instructions in Studio 5000 logic designer to move 2 different values in the same destination tag N7[190]. Two...
4,520
Hi I'm working with twdlmda20drt and i was wondering if there is a move instruction in twidosuite cause i cant find it and i may need in the...
2,064
Hi all I currently have a system where data is scanned into a system and in the fc is a move instruction which I move a '00' on the input and...
1,864
Hey I'm new to rs logic 5000 I have the basics but I'm getting confused with this mvm instruction. Can anybody bum it down for pls Thanx in advance
4,927
Hello everyone Im using SoMachine Basic V1.5, the PLC is a TM221CE16R with analog inputs, I also have a TM3A2Q (analog out) I have everything...