Motor Locked Sinamics S120
bornwild
May 2010
Riyadh
429
We have a couple of S120 drives which are rack pinion system,which moves forward and back ward (linear motion only) . The drive shows Fault 7900 3 times per shift or sometimes more. The drive is commissioned for 6 -7 months. As per operator, it happens only during forward movements. What should I check. I checked the help file and it says to check below. I have increased the motor locked time but still the fault still comes up. Kindly advice
You should set up a trace and monitor the current and torque
Has this occurred since day 1 of your startup?
I agree with JRW. You should also track encoder position and speed. I've had that fault before when the encoder wire had an issue; same thing where the machine was commissioned for months and it would happen randomly.
Actually I am in remote support and I asked the customer to check the encoder wire for any damages. Was your cable damaged? or is better to change the wire to rule out any issue
Set your measure value acquisition to endless trace
download just the trace and start the trace with the arrow button
Watch the trace as it move back and forth
Can you do a screenshot of the expert list starting at about p300? and about the next 30 values down
That will tell us all the basic motor nameplate data
Your trace was there, but is now not visible.
My comment - you need to show speed demand as well as speed feedback - it would appear you have a synchronous motor so you can replace the current feedback with speed demand.
Hope you are doing well. Currently, I am involed in a revamping project. It requires to stop a mixer at specific postion. For the detail, this...
170
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
233
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
313
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
163
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
368