Make an HMI convert from inches to PUUs (numeric input) before writing to servo drive
ivanbenitezmx
Apr 2024
Mexico
Hello all,
I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI and servo drive (RS-232), I can write and read parameters through the HMI to the drive.
Right now I'm setting the positioning command via PUUs, but I want to make the operators life easier by allowing him to input the positioning command in inches. I was thinking on using a macro command that can do this conversion but I'm not really sure how to accomplish this. So my main goal is to input the length to move in inches but make the HMI write the parameter to the servo drive in PUUs.
Any ideas/recommendations would be much appreciated!
System's equipment used:
HMI: Delta-DOP107EG
Servo Drive: ASDA2 0721 M
Servo motor: ECMA-C10807ES
PLC: DVP28SV11R2
don't know the delta HMI but your post is a little unclear, however, the formula is as below
I do remember using this some time ago, I googled it then & put the formula into the comments of my PLC for reference
//step per inch = (motor steps * microstepping) / (travel at one turn of the motor in inches)
//if microstepping is set at 16 (1/16 on the driver) then and you are using a sprocket and chain with a pitch of .25 inches and 12 teeth on the drive sprocket
//= (200 * 16) / (12 * .25)
//= 3200 / 3
//= 1066.666 steps per inch
//For lead screw that has a travel of .5 inches at one turn like the 5 start 1/2 inch lead screw and using 4 microsteps per step (1/4):
//= (200 * 4) / (.5)
//= 800 / .5
//= 1600 steps per inch
Hey all, First time poster... I'm trying to convert a PBA to FTV but keep running into the same error... "Failed to open project:" I've...
1,476
Is it possible to convert project wincc flexible 2005 to wincc v6.2
1,215
Hi, Im having a practice with a Siemens MM420, using siemens S7 via profibus, im struggling with the status PIW speed ref. I want to convert this...
3,440
Hi, Im having a practice with a Siemens MM420, using siemens S7 via profibus, im struggling with the status PIW speed ref. I want to convert...
1,882
Hi. If this is the wrong forum i apologize.. inserting a Float value to sql... I Got an Error in my scada system (indusoft, VBscripting) I got...
5,020