Loss of Comm between SlC 503 and Compact
Denton
Aug 2015
East London
Hi
I am trying to program Comm loss between a SLC 505 and compact logix that talk each other to stop a machine.
Can you please help:ROFLMAO:
Welcome to the Forum !
Message (MSG) instructions are used to control data exchange between these controllers, and each MSG instruction has a data block that holds its configuration and status.
In the SLC, that's an Integer (N) data file or an MG (Message Configuration) data file. In the CompactLogix, it's a MESSAGE datatype.
Both of those have an Error bit that you can examine in your logic to determine that the message has failed.
You can also use logic that examines the Enable and Enabled-Waiting bits if you want to manually override the timeout features in the firmware.
It's a pretty flexible process. If you post some more about the network type you are using and which controller is initiating the message, folks make be able to give you more detailed advice.
Good Morning , I just recently did a project with several PowerFlex 525 drives. I just recently started getting a F 73 Fault ( EN Net Loss...
24
24,635
Easy, basic question... this is my first time linking 3 ABB vfds to an Allen-Bradley PLC using ethernet IP, and the odva Drive assemblies 123 and...
2,516
Hello, How can I go about setting up a fault bit if I lose comms to an AENTR module? I have several 1734 AENTR modules on my network. Some...
3,443
Processor is a L32E For some reason, I thought that there was a tag member that would give a status on Ethernet communications for a powerflex...
25
15,784
Hello, I'm struggling with intermittent comm loss on two ABB ACS800 Drives, it definitely seems to be affecting one drive more than the other but...
1,724