I have a setup where a ControlLogix 1756-L81E is connected to a rack of Kinetix 5700 drives (2198-P070 Bus Supply, 2x2198-D057-ERS3 dual axis drives). I have connected up 1 Rockwell MPM-B2153F-M motor to the second axis of the second drive.
I haven't used Kinetix Drives in a long time and have never set them up from scratch before.
I have set my IP addresses and can browse to the drive modules. They are connected in a linear topology with the CPU at one end and my laptop on the other. The STO inputs have been connected and it shows up on the drive as both being OK. The CPU is set as the Time sync master.
When power is turned on, the drives start in "STANDBY", then change to "CONFIGURING" state and don't ever seem out of this state. The MOD lamp flashes green.
My CIP axis shows a fault icon and when I look at the axis parameters, I see a Config Fault, and ConfigUpdateInProcess in my axis status. I also see a Module Connection Fault. When I look at my attribute error code, I see 16#000c and 16#0585 for my Attribute Error ID. I have been unsuccessful in finding anything that can tell me what these actually mean.
If I browse to my Module Info for the drive and try to reset it, I get a message saying that it was unable to perform the service due to current module mode. When I look at my axis properties, I see that the axis state is faulted and the safety state is unknown (No motion connection).
I noticed that my network mode is set to DLR even though I have a linear configuration and there doesn't appear to be any way to change it.
I feel like I am missing some simple part of the process here, but I don't really know where else to look. I am also unsure about the encoder connection, as the cable was made up as opposed to being the pre-made one from Rockwell. Could this cause these kind of problems?
Any advice for things to check to get this back on track would be greatly appreciated.
I haven't used Kinetix Drives in a long time and have never set them up from scratch before.
I have set my IP addresses and can browse to the drive modules. They are connected in a linear topology with the CPU at one end and my laptop on the other. The STO inputs have been connected and it shows up on the drive as both being OK. The CPU is set as the Time sync master.
When power is turned on, the drives start in "STANDBY", then change to "CONFIGURING" state and don't ever seem out of this state. The MOD lamp flashes green.
My CIP axis shows a fault icon and when I look at the axis parameters, I see a Config Fault, and ConfigUpdateInProcess in my axis status. I also see a Module Connection Fault. When I look at my attribute error code, I see 16#000c and 16#0585 for my Attribute Error ID. I have been unsuccessful in finding anything that can tell me what these actually mean.
If I browse to my Module Info for the drive and try to reset it, I get a message saying that it was unable to perform the service due to current module mode. When I look at my axis properties, I see that the axis state is faulted and the safety state is unknown (No motion connection).
I noticed that my network mode is set to DLR even though I have a linear configuration and there doesn't appear to be any way to change it.
I feel like I am missing some simple part of the process here, but I don't really know where else to look. I am also unsure about the encoder connection, as the cable was made up as opposed to being the pre-made one from Rockwell. Could this cause these kind of problems?
Any advice for things to check to get this back on track would be greatly appreciated.