How to setup vfd speed based on job per hour
sukigill
Apr 2024
USA
Hello,
I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by supervisor/manager.
Is there any formula or mathematic equation that I can use in PLC so whenever Supervisor wants to change the speed they will just enter how many jobs per hour they want to run on the HMI screen and the PLC will send the heart based on the JPH selected. Please let me know if some one have done this thank you
Should be a simple linear scaling based on y=mx+b. Since 0Hz = 0job/hr, the "b" term is 0. You just need to measure "x". To do that, run the VFD at 30Hz (for example) and note the job/hr. Divide them and that's your ratio. Assuming the ratio is constant across the range of VFD speeds, you would then multiply the ratio by the entered jph to get Hz.
Hi All, I have a FR-V520-3.7K inverter here and I need to locate the software for it. Googling say "FR-SW1-SETUP-WE" is the original software...
3,377
Hi guys, What would be a good choice for a drive or servo in a master/slave setup controlling two sides of a lift? The issue is that the lift has...
2,244
What is everyone's thought on vfd bypass contactor setup? My application is blower pulling air through a pipe and set of critical flow venturies...
23
5,422
I'm not an AB guy, I usually work with Schneider/Modicon. Here's what I have: Controller: ControlLogix 5562, 1765-L62 Software: RSLogix 5000...
2,231
I'm trying to verify a project with a PLC. The Transfer Setup menu item is grayed out and every time I click Verify with PLC, I get an error...
71