GSV rslogix 5000. Time Exception
Zakonenko
Jun 2015
Bolgary
Hello,
I always have problems with GSV.
I have to prepare a sequence in RS5000, which need to operate only at the set time. For example, from 22:00 till 3:00. It is really difficult to do, if the time crosses the 0:00, because I cant use LES and GRT instructions.
Could somebody help me please with it?
Zakhar
Latch a bit on at 22:00, unlatch it a 03:00
The bit can then drive your sequence...
You have two variables, TimeA and TimeB.
Update those from the panel.
Or you could use this if you want it to automatically update as you change the TimeX variables ....
Rockwell has free addon instructions for time and date comparisons.
Go here: https://www.rockwellautomation.com/...d326-9a38-0bf2-7fa8dde97de8;deepLinking=false
and search for
Time and Date Math Add-On Instructions
Overkill, in my opinion. Just importing the T_LIM add-on imports 4 others, T_ADD, T_GEQ, T_LEQ, T_LES. That's a lot of bytes of memory used, the T_LIM data-type is 604 bytes on its own ....
If the op just wants a sequence to run for a set number of hours every day, and be able to change the start and stop times from his panel, the above logic works perfectly.
Personally I would have it as StartTime and Duration instead of StopTime, calculating the Stop hour as StartTime + Duration, MOD 24. That way you can inhibit the sequence completely with a Duration of 0
Thank You a lot!!!
It is also good to add SUB - 1 to the TimeB. Like in attachment
Thank You a lot!!!
Ah Yes ! Because you want it to stop at 6, not 7 as my first code would have done.
But you need that SUB in front of where it is tested in the LIM.
But now you have a problem if TimeB is 0 (midnight), the SUB will make it -1, which the LIM is not going to work correctly with.
This should cure that problem ....
Yes :)
Better MOV in the end
No, you need to make it 23 if subtracting 1 makes it -1.
You can do it with a MOV if you like, or just ADD 24
Hi folks! I'd like to add to my PLC logic a way to detect what failure is my I/O module (PowerFlex 525 VFD)having. My goal is been able to array...
4,472
Hello everyone, I am having an issue with random I/O faults on a ControlNet network. In the logic, there is a GSV instruction with LedStatus as...
5,389
I'm trying to extract the fault status from a CompactLogix L33ER rev 20 and I cannot get the GSV intruction working on the Fault Routine. I...
3,959
I am trying to get the Wall clock time with GSV. I was looking at this you tube video Here, I noticed that the Data type that they picked was...
5,957
Hi guys I have a project in my head that I'm thinking of putting on our machines to help the engineers to fault find ? On our machines we do not...
1,975