I have a unique situation where we have two separate process networks ( plc, HMI, etc only).
The two process networks are are owned by two separate companies which share the same real estate and have conveying control equipment that would need to be split. These two companies were split in a acquisition.
Company A does not want Company B to have access to there network and the other way around. This scenario is only for one year. We are are working on a long term plan to split shared plc I/O into company A's own process network.
Temporarily
Has anyone ever ran into this type of situation. I am not sure if a bridge plc could be put in place between company A and B's plcs to handle the necessary messaging and switches between here to block the access of company A and B data access. I know this probably makes no sense, but here we are. lol Thanks in advance.
Well, you already know it's a thorny problem and without spending days learning all the details and expectations I only have some general advice.
- Start with what has to be communicated between them. That should help narrow the focus.
- having "routable" protocol which means anything ethernet related can be problematic. Consider having a Ethernet/IP to Modbus RTU gateway on each side. then, the only connect between A/B is a serial cable.
- Firewall is easy to get, hard to configure and quite useless unless it's configured properly.
Use a firewall to split the network for a temporary solution but if company A has physical access to the equipment of B and if B has physical access to the equipment of A then you have to split the physical network to be really secure and on the network, you would need to employ NAC network access control so that new devices connected to the network are rejected without pre-approval and any attempts of connection of foreign equipment are logged and alarmed.
I think we may have 10 points of I/O to manage between. Thanks for the input. I will look into this.
Since there's only a few I/O, have you considered hardwiring it from one side's outputs to the other's inputs?
Perhaps a modbus gateway that can support 2 separate networks. All the interaction between network is done inside the gateway. Prosoft makes such a thing, I have used it for a similar purpose.
If you configure the A devices to a different subnet than the B devices, the communication between them will be cut, even if they share the same physical network (cables and switches) and without having to use a firewall
Example:
Subnet A 192.168.1.* Mask 255.255.255.0
Subnet B 192.168.2.* Mask 255.255.255.0
Hi all, I have a studio 5000 project that incorporates a Rexroth Indradrive Cs servo amplifier, a Kistler Joiner, with a maXYmos measuring/control...
31
I am working with a remote rack with a 1771-ASB adapter, and inside Logix 5000 I am trying to find where it displays the status of each of the...
117
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
112
I have a slc500 plc 1747-L30A. Using a communication cable 1747-PIC cable box combination. Running a version of software from DOS on a Windows 3.1...
182