Clearing Out a String Tag
recondaddy
Apr 2006
Atlanta, GA
77
Is there an instruction in RSLogix5000 for clearing out a string tag? I've tried COP with a zero as the source and the string tag as the destination with a length of 1. I get
"COP, Operand 0: Invalid kind (tag, literal, or expression) of operand."
I've also tried MOV with a zero as the source and the string tag as the destination. With that, I get
"MOV, Operand 1: Invalid type."
I can't really use DEL because I never know the exact number of characters that the string will contain.
Anyone have any guidance?
Yep. I figured it out. Didn't realize that you needed to write a zero to the .DATA[0] element of the string tag:
MOV
Source: 0
Dest: MyString[1].DATA[0]
Or, I guess a CLR would work just as well. Thanks for your help.
The error message is telling you exactly what you're doing wrong, that is, trying to move a numeric value into a string. If you'd use a null string (string = "") as operand 1, I bet it would work.
CLR or MOV will only clear one character. To clear all characters from the string use FLL.
FLL,0,string_tag.data[0],x
where x is the length of the string.
How does one get a null string when there are no String Literals? Just a string that was never assigned anything
P.S. AB Sucks, Long Live IEC61113-3
P.P.S. I have to us AB :cry:I hate it so much. :cry:
P.P.P.S. I was in High School when this thread was started...
Adding to that you can use FLL with 0 as the source, the STRING as the destination, and 1 as the length. It will fill the LEN and every SINT with 0 and blow the whole lot away.
You make one. If you NEED a blank string, create gsBlank as a STRING, leave it empty, and then make it a constant.
:facepalm:
All this time (literally decades) I've been doing it the "hard" way by addressing both the LEN and DATA.
I think we might be seeing more zombie threads this week than usual. But hey, never too old to learn.
I have been working on so many serialisation projects over the last few years that doing things with strings that a PLC should never have to do has become commonplace :(
#Databases
#Industry4.0
#BigData
:mad:
Im with Bernie. I use a blank string and COP.,its probably not the most smallest use of memory but its easy and memory is cheap lately
So apparently at least in v30+ this is perfectly valid......
Which means RS 5000 does have string literals.......
Which mean all these other hacks are useless.
Hello all - I have a string tag that is a member of a UDT that I would like to clear within a Structured Text routine - but cannot seem to get it...
7,343
RSlogix5000 - Here is what I would like to accomplish and what I am running into. Currently this is a scanner ASCII gateway to PLC set up. A)...
3,996
Hi I am using a SLC 500 and a lot of string handling. I need to copy a NULL value to a string table eg. ST16:0. How do I do it?
5,102
I'm online with a 90-30 using PAC ME 9.8 No one has gotten online with this PLC for many years and the the I/O fault table has a total of 1209...
3,006
Using an L81 - I have the arrangement below that will try the Ethernet Radio first and if that fails use the Cellular Radio. The Failover works...
3,383