APC SM1000c to SE M340 modbus TCP comms
kuckphoto
Nov 2018
Kentucky
Hi has any one linked a Schneider Electric Smart UPS to a PLC through Modbus TCP? Supposedly it can do it, I'm told. but I'm not entirely sure how. I know the modbus addresses that I want to bring into the PLC but being fairly new to Schneider and Modbus I don't know how to proceed.
We're using a BMXP342020 and a SMT1000C
Any help or a point in the right direction would be greatly appreciated.
Since you don't have a NOC or NOE comms card in the PLC rack, you'll have to do this using READ_VAR function block in the PLC through the processor ethernet port.
Its a challenge getting it working the first time...
Do a search for READ_VAR on this forum, there was a chap recently trying to do something very similar, but to some red lion remote I/O.
Timeout GEST
The timeout value in the GEST control block should be set to a nonzero value using a MOVE before you hit the read_var the first time. It looks at the timeout when it starts the communication. Zero corresponds to an infinite timeout. If there is a zero in that GEST element and your read_var is not successful it will probably hang up and you will have to cycle power on the processor. Loading a nonzero value after the fact will not recover the read_var.
Triggering the read_var seems to not be very well documented if you don't want it to go continuously. Too many Read_vars going at one time may lead to socket count problems. Expose the EN pin on the block and one-shot it whenever your want a communication to start. When I've had several read_vars that need to be sequentially triggered I've used SFC to sequence them.
I'm not sure where the term 'GEST' came from. I suspect it's an abbreviation for something in French.
Read_var is subject to the usual Modbus issues with address offset versus communications index. The result is that you may have to adjust your register number up or down by 1 to get the correct data.
Older Modicon software could not put the return of a communications command into an 'unlocated' variable. It had to go into register space. Now you have the better option to go into an unlocated. You will have to turn a project option to allow dynamic array indexing - I forget the exact term for the option.
I wish you well with your project.
This is a program in a machine that has been running for about 7 years without any issue like this. We have a master servo (the machine's main...
1,173
If f.i. the slave axis has to start the camming not from the beginning of the cam but somewhere in between, the parameter 'cam lock position' has...
1,443
In a Siemens controller when I have a cam where f.i. master- and slave position is absolute, when the the camming is started the slave will first...
1,608
Please tell me how to correct two alarms on APC Galaxy 3000 UPS: #1: Cooling fault (Cooling liquid level is low) #2: End of batt service life Due...
1,458
Good Morning , I'm having a problem with a Kinetix Servo MAPC instruction. I keep getting a #85 Fault. Could you give me some...
1,706