Allen Bradley 1734-AENT issue
Are the original and replacement modules from the affected date range in the technote that @MikeyN posted? Even if they're outside that range, I'd reach out to Rockwell and your local distributor.
Yes, i saw this, my modules are from 2020. How i suposed to update frimware on each modules? I can change on ethernet module but how about all of them?
According to the TechNote, if they're in the date range specified, they need to be replaced. I haven't worked with Point IO much, so I don't know if their firmware can be updated. I think @jstolaruk's suggestion is for the modules that can be updated (PLC, comm modules, etc.). Personally, I would not upgrade the PLC firmware unless necessary or unless you want to harmonize with other systems in the plant. It may be worth trying as a diagnostic step if you can, though.
Some confusion here. I did not suggest to upgrade the firmware in the safety modules, I suggested updating the EN2T firmware. I also recommend updating the Studio s/w and running the latest patch update.
If there is a problem with the safety modules, I know from experience (bad batch of 1734 safety outputs modules) that RA takes it seriously and will want to get them swapped out as soon as possible.
We have a lot of POINT-IO modules in various places all over our machines. Occasionally one of the daisy chained cables between our 1734-AENTR...
1,732
Good Morning! I am new here and have limited experience in working with PLCS, and desperation has brought me here with a problem, hoping some of...
2,903
Hello, I want to connect 1769 L18ER PLC with 8 number of 1734 pont IOs. 24V Dc 8 Channel Sink Input Module: 3 nos 24V Dc8 Channel Source Output...
7,749
Is there any reason to match revision exactly to what was installed?? Lets say I have a OB8 card and its 3.022 revision. Is there any reason not...
2,156
I have an AB 1769-L32E compact logix controller connecting to a 1734-AENT/A remote IO rack. Occasionally, we lose communications to the remote IO...
2,075