Addressing PLC-5 16-Slot Chassis as Remote I/O from ControlLogix
sanger
Nov 2005
Toronto
172
We have a PLC-5 with 16 I/O Modules in a single chassis. 1-Slot addressing is used with a 8) 16pt-Input and 8) 16pt-Output modules.
The I/O modules are in a scattered arrangement .
e.g. IIIIIIOOOOOIIOOO
We are replacing the PLC-5 processor with a 1771-ASB Remote I/O scanner and addressing the rack from a ControlLogix processor with a 1756-DHRIO module.
Since the Remote I/O scanner only has 8) 16-bit Input and 8) 16-bit Output data words available how will it map the remote modules to the data?
Will it automatically consolidate all the input modules together into Rack_1:I: Data[0-7] and the output modules into Rack_1:O: Data[0-7]? What would happen if there were 9 Input modules and 8 Output modules?
From Chpt 8 of the DHRIO manual
The 1756-DHRIO module scans the remote I/O devices as they appear in the ControlLogix controller’s controller organizer. The entries in the organizer represent logical adapters. The physical adapter modules on remote I/O may act as several racks. This depends on the addressing mode of the physical adapter and chassis.
Add a new entry in the I/O Config for the second logical rack
OG
I talked with Rockwell and they verified that a rack with 16-Modules and 1-Slot addressing will appear as 2 separate racks to the Remote I/O scanner.
e.g. If the rack is addresses as Rack #1 the scanner will see Rack #1 and Rack#2 each with 8 Modules.
I can confirm (having done this exact scenario many times) that Operaghost is 100% correct.
Basics : your 16-slot physical chassis can be configured to be 1, 2, or even 4 logical racks, depending on the addressing mode set by the chassis switches.
1 rack if 2-slot addressing
2 racks if 1-slot addressing
4 racks if 1/2-slot addressing
What you must do in Logix5000 is to add an entry for each and every logical rack.
As stated, that is the only way you will get the tags in the Logix5000 database to "communicate" with your I/O devices.
I have a DL06 PLC from Automation direct and I am trying to learn how to use the expansions slots in my program. Coming off of allen Bradley...
20
6,245
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
412
Hi All Working with Tia v16 on a PLC 1515F I am getting older by the minute, beating on indirect addressing for a DB I have a DB with 65 row of...
3,794
Hello I read your info about modbus addressing with %MW register. I have a PLC with registers PLC ADDR: MW4513 and the machine constructor write...
7,165
Hello guys, This works: L P#DBX 30.0 LAR2 But I need "DBX 30.0" to be input parameter to the function. I made pTag variable with data type...
19
6,414