A little Ladder logic help
BeepBob
Jan 2023
Oakland, CA
110
Hello,
I am trying to replicate a piece of logic on the PLC5 onto an SEL RTAC. I am using ladder on SEL and FBD. I am having issue on the ladder portion in SEL when it comes to timer timing and the SR block. I do not have an RTAC yet to test so seeing if anyone can spot logic issue.
The off logic is identical to the on logic. Screenshot added
1. I made network 1-4 , I think it is identical in functionality to the PLC5 code, except for the timer timing, I do not know why SEL does not provide a timer timing attribute. Reason I made 5 networks (rungs) is because SEL close branch...is weird
2. Network 5-6, I am trying to do the logic using an SR block, I think I can do the timer timing by accessing the T1.IN bit?
1) the R_TRIG instructions need to use different memory structures; in the first image all of the R_TRIG instruction use the same R_TRIG1 memory structure (bit?), which I am pretty sure means only the first one will fire. Solution is either to use a different memory structure for each R_TRIG instruction, or to have just one R_TRIG instruction that writes to an intermediate bit "oneshot" that is 1 on the rising edge of the (BST XIC SAB1_TDO NXB XIC SAB2_TDO) parallel branches, and then use XiC oneshot at the front end of the four rungs that set or reset GATE_TDO_ON and GATE_TDO_OFF.
2) GATE_TDO_OFF can be removed from that logic and replaced with the equivalent of XIO GATE_TDO_ON OTE GATE_TDO_OFF.
I think I figured it out . Using only 3 networks. SEL makes you put in the R_trig...then it will allow you to do a parallel contact..ladder_1.jpg
Also, XIC theTON.TT is equivalent to XIC theTON.EN XIO theTON.DN, if SEL does not have .EN then you can write a bit with a coil on a branch in parallel with the TON.
What happens if the SAB1_TDO or SAB2_TDO value returns to 0; doesn't that shorten the .TT-driven pulse?
Hmmm, I am not sure. Only the FBD have the 'TP' block. In Ladder there is only the TON block.
I think what I got now looks ok. The SEL engineer says I can use an XIO on the TIMER.Q to indicate that the timer is timing.
This reads cleaner to me, at least the last two rungs. I am pretty sure it is essentially equivalent; it does not maintain state across a PLC mode change.
It should be trivial to convert to FBD, since it is all ANDs and ORs.
Sorry, the second rung is wrong in that attached image. This should be correct.
SAB12R is the result of the rising edge on the on the OR (parallel XICs) of the SAB1_TDO and SAB2_TDO bits.
Very familiar with the SEL RTAC's. Never saw them used for anything other than power distribution and control. The local power provider uses them at all their sub stations. Is this a gate at a power station?
Remember to mind the time units of the timer.
I notice T74 timer is time base 0.01 and the preset is 10 so that is 0.1 seconds and the T1 is T#1S may mean it is 1 second.
Yes, we have them at our substations. But the decision was made by the top to go ahead and use them for general-purpose. Something about lengthy acquisition bureaucracy if anything else...
Hi, Need a little bit guiding using SISTEMA software. As I understand a subsystem consist of components and are the same category. I'm confused...
2,674
Good morning everyone, I've got 2 servo driven axes that each use a Heidenhain glass slide to the motion controller for position and velocity...
1,417
RSLogix 500, what is the little image next to the ladder in the project tree? it looks like a little blue bug with a red dot on its back. just...
2,064
Hi everyone, trying to get data out of a digital encoder that is little endian into my Siemens S7-1200 controller that is big endian...it's an...
3,442
Hello all. I was starting to get into a new project (that will probably never see the light of day because $$$) at the plant I work in and...
26
5,616