4-20ma Current Transducer vs True RMS Clamp Meter
justblaze
Supporting Member
Oct 2012
New York
21
I purchased a 4-20ma AC Current Transducer, it can be set to 0-100a, 0-150a, 0-200a. It is not True-RMS.
This is connected to a panel meter and I wanted to know why the measurement from this equipment is different than my True-RMS clamp meter.
I was testing both out on a 120v AC branch circuit. The current transducer and panel meter were showing 6.8 Amps but the True-RMS clamp meter was showing 7.2 Amps.
To me a difference of 0.4 Amps seems excessive. This was even with the current transducer on the 0-100a setting so it would be as accurate as it could be.
The scaling was set correctly on the panel meter...On the feeder supplying the breaker panel there was about 50a of current on L1. The True-RMS meter and the current transducer & panel meter differed by an amp on this.
Is there really that big of a difference with a True-RMS measurement? Or could it be dirty power in our building? Maybe the AccuAmp current transducer from Automation Direct is that inaccurate? It's made in the USA :/
I think you are better off posting this on the main board, so everybody can see it :).
Other than that, if one meter would show peak current, one would expect the RMS to be less than that, not more?
I'm using an AB 2085-OF4 module for outputting process current control to various VFDs. When using this device, I have the channels configured...
3,066
Dear All, I want to use a 4-20mA output from Omron AO module, so I did the following configuration: PLC used CJ1M-CPU22, rack 00 CJ1W-AD041, rack...
5,055
Hi, What is the reason behind the 4-20mA current as a standard signal for transferring data? Well for starters, we choose current over voltage...
6,899
Hi, May i know the how to know the minimum voltage to drive a analog input card. I'm connected to 4-20mA channel for 4 wire, supply voltage from...
6,679
Hi every body. I have some problems Easidew On-line Hygrometer now I used a Easidew On-line Hygrometer to meansuring humidity of air , It have a...
2,821