1734 aentr
Stuwertz
Feb 2018
49
Dear sirs ,
One of the 1756 EN2T MOdule communicated to three Ethernet adapters (1734 AENTR) . Normally During running condition every 10 mins Ethernet adapters point bus status and network status flashing red on all the three Ethernet adapters. Then again getting healthy automatically and cycle runs . Then again error came .
Corrective action taken .
1. Network cable healthy condition
1. I replaced and shuffled adapters .
3.three Ethernet adapters powered by three seperate 24 v power supplies
4. I Replaced 1756 EN2T
Need your advise to solve this issue . Thanks.
Welcome to the PLCTalk Forum community !
According to the 1734-AENT user manual, that is consistent with the network connection timing out.
I would examine the Ethernet switch carefully to see if it is also experiencing a disruption.
Does this happen exactly every 10 minutes, or approximately every 10 minutes ? How long is the duration of the disruption ?
Hi sir . Thanks for your immediate reply . This issue not exactly every 10 minuets. Sometimes it’s running without issue for maximum 15 minutes. Sometimes issue appeared every 2 to 3 minuets.
The EN2T module connected to the AENT adapters through linear topology. ( without switch)
Thanks.
Are you certain all three AENT adapters have different IP addresses? And are they static IPs?
How long has has the system been running?
Is there anything else connected to the network?
If you look at the diagnostic screen for the 1756-EN2T, what errors are you seeing?
EN2T and 1734 AENTR ( 3 no’s ) . The system should run continuously to convey the product. Nothing else connected on the network.when the network status and point bus status flashing red the link down only shown in the EN2T card . The link led on the EN2T card not blinking that time .
Let me rephrase that. Is this a new system or one that has been running for awhile? Can you see the diagnostic screens on your PC, either on the web page or the module setup in RSlogix 5000 / Studio 5000?
Actually this is not a new system . This system running for last 1.2 yrs . Now only we face this issue . In pc it shows connection timed out . In web page screen not able to find any error message .
When you look at the web page, check the diagnostic counters for collisions or errors. How long is the run of Ethernet cable between the devices and are they ran separate from power sources? You need to find out what changed.
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
365
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
557
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
544
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
317
Hi there! I've been looking for some fault codes table for the 1734-AENTR adapters, since I'd like to show a message in HMI with some...
589