$115 plc-restart running, how to fix
From memory it can be a couple of things (many years since I used S5 & OP) but check the cable $115 usually means it's not communicating.
Other problems that I know of, the communications I believe uses an FB & datablock are you sure your PLC is running & not lost it's program, the OP17 could be faulty or the PLC com port, the interface I assume is AS511 programmiing port.
If the program is not running there will be at least a red indicator (STOP) led flashing or the RUN led (Green) will not be on, so this is a good indication that either there is a fault on the PLC, run switch not in run position or program lost (however, if the program has been lost & a complete restart done then the PLC could be in run mode but unlikely from memory), You will need Step5 software & a 232 to TTY lead to connect to the PLC, this PLC is well beyond it's useful life & spares or software is not generally available from the supplier. The HMI probably was programmed using protool so that software would also be needed. If the program has been lost then without the original source file or at least a copy taken from the PLC it would need to be re-written probably would make sense to upgrade anyway.
This PLC is probably more than 20 odd years old so the backup battery would probably the cause of a lost program unless the program is stored in an eprom (plugged into the front of ther processor) these from memory are orange for eprom & grey/white for ram. To be honest, if you do not have the software & experience to go-online then your only option is to get someone who has the skills to diagnose the problem.
Hi everyone. I'm trying to read values from a Loadcell with a 2080-TC card. I know the 2080-TC is a thermocouple card but it reads millivolts that...
63
Hello All, Please direct me to post to the right page. I am really new to PLC, and want to find a tutor who is familiar with Automation Direct's...
65
I've come across a system running omeron cx-programmer version 9.42. Am I going to need to find a legacy version of the software to edit and...
45
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
86
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
87