Reverse engineering CCW PID instruction Micro800 Micro810 Micro820 Micro830 Micro850
Summary
The [PID] instruction in CCW for Micro8xx PIC uses the Dependent Gains form of a PID algorithm. However, the [PID] instruction does not work as advertised. Specifically, the tuning parameter members of the PID_GAINS object used by [PID] are not all consistent the with the canonical/conventional meanings of their names. If pidgains is a tag in CCW of data type PID_GAINS, then its members have the following meanings:
  • pidgains.Kc - Controller gain, units of dCV/dError
  • pidgains.Ti - Integral time, units of seconds (s)
  • pidgains.Td - Factor for calculating a first-order filter time constant, units of seconds-squared (s**2)
  • pidgains.FC - Derivative time, units of seconds (s)
    the product (pidgains.Td * pidgains.FC) is the CV output filter time constant
Note specifically that
  • the .FC member of PID_GAINS is not the filter constant that the CCW documentation claims it to be;
  • the .Td member of PID_GAINS is not the derivative time that the CCW documentation claims it to be.
Refer to the link in Post #1 for more detail.
Hi all, I am a young apprentice who knows a very little amount of PLC and don't know how a system works properly yet. my task I have been given...
19
5,406
1) perfectly legit. Company out of business and hardware dying and customers left hanging. 2) This is hard as heck w/o descriptions (ladder...
3,219
I am reverse engineering an old PanelBuilder App (don’t ask!). On some programming screens, the function key tags are shown to me matching the...
2,375
Do you know any simple ways to trace out logic and document it in an easily digestible way? I just spent about 3weeks tracing out logic in...
5,838
I have a customer that wants to convert about 7 to 10 1398 Servos to 2098. They have both PDM and DDM versions. They would like to standardize...
3,007