Selecting fuse size for servo amplifier
dearannie21
Aug 2017
Illinois
I'm working on Mitsubishi MR-J5-70A amplifier, and need some advice on selecting fuse size.
Main power is 1ph 240VAC, and in the manual, it says that for main power, 1ph 240VAC for rated current of 6.5A and for controller power, 1ph 250VAC with rated current of 0.2A.
Is it ok to use 6.5A fuse for main power and 0.2A fuse for controller power?
or is there any calculation related to selecting proper fuses?
Thanks,
With drives or servo amps, I normally find circuit protection recommendations in the manual and follow those as closely as possible. Often, the rated power usage doesn't account for inrush current and if you use the breaker or fuses recommended by the manufacturer, you have something in writing to point at in case something does fail or trip and your decision receives scrutiny.
I am working on trying to create a an HMI program where the user can select a value from 1-25 and then enter a string, which will be placed into...
1,103
We had a servo motor feedback cable get damaged recently and we want to order a replacement. The current cable is a custom made cable, and we...
908
Not sure how to word the title but here's my scenario. We have a carriage that moves at high speed with an energy chain and the cable bends in a...
2,885
Hello plctalk, new guy here. I have an application that I'd like to present for your considered opinions so I can figure out what hardware I...
2,541
Hi, I frequently demonstrate automation product (that we make) to various customers. The system uses an AB7007 Anybus gateway that connects to...
5,371