I'm in the process of replacing an existing powerflex 40p. The old one died with no software backup but we did have a printout of the parameters so we are programming from CCW with that. All of the parameters took except for one, P038, Speed Reference. Being the new drive was defaulted prior to installation, its currently set to 5-Ethernet, when it should be 9-Positioning. In every way I can think of, I tried changing the parameter, even to other values, and nothing works, it always immedietely reverts back to 5-Ethernet. Has anyone seen this before and know of the nuances of speed ref parameter?
Currently Im using CCW, but I also tried within the logix project, online, offline all via ethernet.