Siemens s7 to controllogix via ethernet communications
JohnJPhillips
Jun 2016
Illinois
30
Anyone ever set up communications like this? Trying to assist a plc instructor with making a lab up for a local junior college. They have both racks and your standard modules, but just looking to get enough information together to start tinkering.
I've seen an EWEB module for the controllogix rack being suggested or a red lion protocol converter.
Any help would be appreciated!
I would ring Siemens up and ask whether they can share the GET_R and PUT_R function blocks with you. It's the exact same functionality as the typical GET and PUT functions but for Rockwell.
I tried them already to communicate with a CLX in V20.04 or something like that. They were very very easy to set up.
Hi John,
I'm working on a project now communicating between 6x ControlLogix/CompactLogix and 2x S7 plc's. If you're using TIA Portal there is a T_COMM block for the Siemens side and an Add-On Instruction for the Logix side. Take a look here https://support.industry.siemens.co...ol-system-(clx-glx-controller)?dti=0&lc=en-WW
We've just completed testing on our project and it works a treat.
If you're using the old S7-300 range for the Siemens side you'll need to use a protocol converter like the Red Lion unit which works but is rather slow, or there are other standalone alternatives like Echochanger, Prosoft PLX32-EIP-PND, or you could use the Prosoft MVI56E-SIE which sits in the ControlLogix rack. I'm sure there are others.
Hi John,
Hello Sir,
i connected my compactlogix controller and s7 1500 cpu with a ethernet cable. i want to import the tags into the tia portal that used in the copactlogix program.how can i import the tags?
please help.
We have a situation where we have a ControlLogix PLC that we need to connect to existing Siemens RFID readers using RF180C units. To do this we...
1,094
I have a Siemens LMV52 with an AZL and am trying to read some values to display on an HMI. The PLC is an Allen Bradley Contrologix L81E. Using...
1,890
Controlling about 6, 6SE70 AC drives with ControlLogix over Devicenet. Can not find where the speed setpoint is being written too in the Drive...
1,360
We are replacing several Siemens S7 PLC's w/AB ControlLogix PLC's. Does anyone make a simple adapter where I could plug the connector of a S7...
1,886
In a new facility that we are designing, some skidded equipment is being delivered with S7. Our plant is primarily Rockwell ControlLogix. In...
6,665