S7-300 & YASKAWA A1000 Profibus PPO5 BB(Base block) Alarm
Hasitha
Dec 2015
colombo
44
The matter is im facing a BB alarm while i try to communicate yaskawa A1000 & S7-300 by profibus PPO type 5 method.
I have changed my first control word into PQW30 and also i have transferred W#16#F into PQW30 inside of OB100.
My Drive parameters are as below.
F6-30 = 10
F6-32 = 0
H1-08 = 0F
B1-01=3
B1-02=3
Also please be good enough to check uploaded images below for my S7-300 configurations and result variable table.
PPO5_Hardwear_Configuration.jpg PPO5_PQW30_CALLING.jpg PPO5_Variable table.jpg
Check the drive settings usually the base block is triggered from one of the programmable inputs the can be setup as N.O. or N.C. if the input is not on it triggers the base block.
H1-08= Multi-Function Digital Input Terminal S8 Function Selection (External Baseblock Command)
into 0F ,
F= Through mode /Select this setting when using the terminal in a pass-through mode. When set to F, an input does not trigger any function
in the drive. Setting F, however, still allows the input status to be read out by a PLC via a communication option or
MEMOBUS/Modbus communications
H1-08 = 0F is my setting and still BB appears :(
While input 8 H1-08 is base block it is default set up as a N.O.
this would require the input to on for base block but if your drive has input 8 disabled it is possible that another input is setup for base block N.C. that would require the input to be on to turn off the base block
Check the set up of all the inputs any one can be setup for base block
it mat also be possible to set the base block through the communication card just like you give it a run command check the network manual
Hi guys. I have some problem.I want to use AB PLC Control YASKAWA servo motor through MP3300 EtherNet/IP Communication Module. Now I download...
2,133
Dear Superiors,📚:wizard: I'm new for s7-300 and yaskawa v1000 drives communication via profibus. My aim is to find how to run the drive or...
1,747
Hi All~ I have a case (designed by my boss But he has left the company) Please refer to the attached picture...
2,378
I need to design a flying cutoff system with MP2300 - MECHATROLINK-II communication SGDV Servo drive SGMVV Servo How should I read the line...
2,555
Hi , I have to do some modification in YASKAWA MP2300 PLC but in that existing backup ,some blocks are protected. How can i un-protect that...
1,397