Flow Totalizer S7-300??
Viggen
Nov 2007
Oslo
Hi there!
I have used the search button for help to find some solution`s
to make a totalizer for flow.
I did see many solution`s but all the answers are in STL.
Because i allways have been using LAD for programming the STL is greek for me.
Is it anybody that wants to make an example for totalizer in ladder??
input is 4-20mA
Flow rate 25000kg/h
ps. Sorry for my bad english
regards
Eivind
Here's a very simple and sometimes accurate enough way:
0 - 25000kg/h = 0 - 6.944kg/second
So: scale 4-20mA input to floating point value of 0 - 6.94kg/sec
Then: use 1 second timer to snapshot "sample" 0 - 6.94kg/sec floating point value and move/add it to another floating point register "Total."
Every second the total will grow based on the flow rate at that 1 second snapshot.
This is primative but works and CAN be optimized with the usage of scan time considerations and time slices but that's more complicated and PLC specific.
This is my implementation.
I like using cyclic interruption blocks such as OB35 which is executed every 100 ms (default)
You have input 4-20 mA = 0-25000 kg/h
25000kg/h = 6.9444 kg/s = 0.69444 kg/(100ms)
So, first scale your input (in S7-300/400 it is integer range 0-27648) to 0 - 0.6944 with standard FC105
Second, just summarize current input value to current totalizer and that's it.
I'd like others to express their opinions about this solution.
Hi; We installed an orifice plate type steam flow transmitter which configured to give 4-20mA signal correspond to 0-9ton. I given that signal...
24
5,605
Hello. I wanted to write the logic of the flow totalizer and the flow itself for self-education in RSLogix5000 V20.01 software. After reading the...
7,598
Hello I was needing some guidance on communicating and setting up a totalizer from a flow meter in the PLC. The PLC is a AB 1769 Compact Logic...
1,783
Hi all, I am kind of new to PLC programming and I am currently trying to learn all this fun stuff by myself. I got myself a productivity 2000...
24
4,737
hi, so i m very new to plc programming.Below is my requirement I have to create a program folder for totalizer with individual FBD routine for...
17
4,261